Thread: non gfci protected outlet
06-09-2009, 04:31 PM #1
hey all
business is booming here--turned away a few---yeah
had a new build today and had this outlet in laundry room, near sink and a gfci outlet at sink, but outlet for washing machine left of sink was not gfci protected. shouldn't be--it was only two feet from water
thanks
charlie
06-09-2009, 04:41 PM #2
Re: non gfci protected outlet
I personally do not call out receptacles intended for "washer" connections to be GFCI protected. Those close or above a laundry sink I do.
06-09-2009, 05:07 PM #3
If the area has adopted the 08 the receptacle for the washer would reqiure GFI protection within 6' of the outside edge of the sink. There is no exception for a simplex receptacle.
06-09-2009, 05:22 PM #4
RICK
would you classify this one close enough, as your post stated
charlie
06-09-2009, 05:35 PM #5
Re: non GFCI protected outlet
06-09-2009, 07:06 PM #6
Charlie,
If the receptacle (outlet) is within 2ft. from the rim of the sink as you mentioned, it should be GFCI protected.