Results 1 to 10 of 10
07-13-2009, 05:11 PM #1
Unknown items in electrical cabinet
I know I've not been around the block as some of you (that's a compliment)
These items were installed in the bottom of the cabinet; they were wired in. "Motorola" was imprinted on the side.
I'd appreciate any help.
Bruce
Similar Threads:Bruce Thompson, Lic. #9199
www.TylerHomeInspector.com
07-13-2009, 05:49 PM #2
Re: Unknown items in electrical cabinet
I think they are surge protectors.
07-13-2009, 06:56 PM #3
Yes, surge protectors and they should be mounted through the exterior of the cabinet, *not* "in" the cabinet as you see them.
Also see a lot of multiple tapped neutrals.
07-13-2009, 08:31 PM #4
You DID pick up on the fact this is a FPE panel, right?
07-13-2009, 08:34 PM #5
Yep, gave them my standard FP line and recommended a new panel...hopefully taking care of the doubled-neutrals and the surge-protectors mounted in the cabinet
Thanks for all of the help. I appreciate you guys.
Bruce
07-13-2009, 08:37 PM #6
Good to see that dirty old US FPE panel is surge protected.
The neutral bus appears to be bonded to a ground on the right with several white wires.
Amateur workmanship?
07-14-2009, 04:13 AM #7
07-16-2009, 05:48 PM #8
I dont know guys,,,is that the buss they are connected to or the mounting screws to the back plate? In all my years I dont think I have seen one quite like this. I give JB an A+ for uniqueness!
07-16-2009, 06:02 PM #9
07-16-2009, 06:27 PM #10
Well...now that I have cleaned my bifocals I think JP is right again!