Results 1 to 16 of 16
07-22-2009, 03:49 PM #1
An interesting electrical problem
This puzzles me... When I turn my hood fan on for the stove, it resets the stove, like a complete loss of power for a split second, if your cooking something it will cancel the cooking and reset the clock to 10:40 I am at a loss here and not looking forward to digging into my recently renovated kitchen. Any thoughts would be greatly appreciated.
07-22-2009, 04:15 PM #2
Re: An interesting electrical problem
Sounds like something is overheating. the clock is just going to a default setting.
Best
Ron
07-22-2009, 04:53 PM #3
Is this fan integral with the stove (like a Jenn-Air) or is this an independent hood that is suspended above the stove? If a part of the stove, it sounds like a loose electrical connection somewhere within the appliance. If separate from the stove, then I dunno. That would mean a phone call to an electrical contractor.
07-22-2009, 05:06 PM #4
Does the range hood have a light? If so, turn on the light first and observe if the brightness drops when you turn on the fan. If it dims noticably, it may be that the fan motor is causing a significant voltage drop at start up. The clock on the range is resetting because of this voltage drop.
Is the fan variable speed? You can lessen the drop by starting the fan at it's highest setting.
Is the fan free spinning? Is it possible that the fan has obstructed movement?
These are just a few things to check first. My bathroom fan didn't work when my house was remodeled. When I took off the grate, I found that the installer didn't remove the packaging material.
07-22-2009, 05:44 PM #5
New appliance?
Call for warranty repair.
Joe described some possible causes, but only if that is built-in with the stove as Gunnar asked about.
If the range hood is separate, I can't see it causing the range to reset the clock unless you have some really poor connections someplace - really poor connections.
07-22-2009, 06:21 PM #6
Thanks everyone for your responses, i'll give some more information as was asked.
1. I turned the light on and checked for dimmer and there was none checked on both high/low light and fan settings.
2. new appliances. Yes and we have already had a maytag repair man out who replaced the digital panel and brain.
3. poor connections are very likely these are poorly built condos, as the picture below illustrates this electrition didnt have much regard for safety or pride in his work.
4. it is not a built in hood, its stand alone
Yes this is my breaker box, FPE stab lok
07-22-2009, 06:57 PM #7
poor connections
FPE panel (which itself has poor connections where the breakers are supposed to stab into and lock into the bus bars, frequently the breakers will pop out in your face when the dead front cover is removed.
Take that door bell transformer out of there, no way is that supposed to be in there nor is it allowed to be in there. And in that small and tight panel, I am amazed that it has not grounded out to the bus bar.
I would invest another $1,000-1,500 and have an electrician replace the panel. Your problem just might go away with that only.
07-22-2009, 07:15 PM #8
07-22-2009, 07:24 PM #9
07-22-2009, 10:58 PM #10
Also gotta love the 120/240 circuit fed directly from the lugs!
07-23-2009, 12:02 AM #11
07-23-2009, 03:31 AM #12
07-23-2009, 03:36 AM #13
07-23-2009, 04:06 AM #14
As others have said, a bad connection.
Is the stove gas or electric?
If gas, are the stove and vent hood on the same circuit?
If so, check the netural connection on that circuit.
But in any case, you have an FPE Panel and need an electrican to check it out( replace it).
07-23-2009, 06:09 AM #15