    Default Service drop clearance
    Does the minimum 3ft clearance rule apply (roof is greater than 4:12 pitch) when the SE passes over other portions of the hip roof? The actual position of the mast is within 4ft of the roof edge. Note: The attached picture does not show the "sag" very well in the SE but it is below 18 inches at the ridge cap.
    Default Re: Service drop clearance
    2006 IRC
    E3504.2.1 Above roofs.
    Conductors shall have a vertical
    clearance of not less than 8 feet (2438 mm) above the roof
    surface. The vertical clearance above the roof level shall be
    maintained for a distance of not less than 3 feet (914 mm) in
    all directions from the edge of the roof. See Figure
    E3504.2.1.
    Exceptions:
    1. Conductors above a roof surface subject to pedestrian
    traffic shall have a vertical clearance from the
    roof surface in accordance with Section
    E3504.2.2.
    2. Where the roof has a slope of 4 inches (102 mm) in
    12 inches (305 mm), or greater, the minimum
    clearance shall be 3 feet (914 mm).
    3. The minimum clearance above only the overhanging
    portion of the roof shall not be less than 18
    inches (457 mm) where not more than 6 feet (1829
    mm) of conductor length passes over 4 feet (1219
    mm) or less of roof surface measured horizontally
    and such conductors are terminated at a
    through-the-roof raceway or approved support.
    4. The requirement for maintaining the vertical clearance
    for a distance of 3 feet (914 mm) from the
    edge of the roof shall not apply to the final conductor
    span where the service drop is attached to the
    side of a building.
    OK, so in English...
    Assuming that the service drop approaches the house at 90 degrees and the roof slope is greater than 4:12, the service mast can be no more than 4 feet in from the edge of the eave, unless the cables are more than 8 feet high.
    Did I get that correct?
    This one has always confused me and sometimes I cannot digest the code.
    "Did I get that correct?"
    Kinda, sorta.
    Must be 8',
    Execpt that 3' is allowed but ONLY when
    Pitch =>4/12
    AND mast is <4' from edge,
    AND SE cable over roof is <6'.
    Forget the 90deg thing.