Results 1 to 15 of 15
Thread: Loose breaker
08-10-2009, 09:29 PM #1
Loose breaker
Heh gang my 1st time posting on the board. Just 2 easy questions. The pictures below look to me like a loose breaker. Just looking for some confirmation. The panel and breakers are Square D. Also, the main risk is arcing which is a fire danger, not to mention a loose breaker can also be a shock risk. Any other risks you would call out?
Secondly, this same panel has a cable wire grounded to a screw on the cover of the box. Please correct me if I am wrong, but I do not believe this allowed, correct?
Thanks!!
08-10-2009, 09:37 PM #2
Re: Loose breaker
You got the double tapped breakers and the white conductors noted also I guess.
08-10-2009, 09:47 PM #3
Re: Loose breaker
Yes, got the double tap, but not the white conductor. The white conductor is connected to a terminal labeled "load neutral" which is ok, right? I believe this circuit is for a 220 hot tub.
08-10-2009, 09:53 PM #4
Re: Loose breaker
The white is on a GFCI breaker. Look closely and you will see the Test button.
Yeah, that loose breaker could be a problem - it could also be an easy fix ... if it has not already arced up the breaker tab, if it has that would be bad news. However, I am guessing that the panel is a CTL panel and that lower right breaker simply cannot be fit on properly, and there is a reason for that ... it is the wrong breaker in the wrong panel.
08-10-2009, 09:54 PM #5
Re: Loose breaker
08-10-2009, 09:58 PM #6
Re: Loose breaker
That loose breaker is not even a Sq D breaker, which is why it is not fitting correctly.
08-11-2009, 03:59 AM #7
Re: Loose breaker
Jerry, your first instinct was correct. Take a closer look. It is a SqD. Might be counterfeit though as it does not look typical.
My bet is that it is a CTL board where someone tried to use a twin breaker.
Cable companies ground to where ever they want it seems, valid or not. Using a cover screw is not a listed application which is why they've come up with some strange contraptions to clamp onto panel boxes.
08-11-2009, 09:18 AM #8
Re: Loose breaker
Peter,
My second post was adding to my first post.
I think that is a non-CTL breaker in a CTL panel, AND, that breaker is not a Square D.
The reason I say it is not a Square D is the width or the raised part, compare it to the Square D breaker opposite it - there is no way that divider piece is going to fit between the non-Square D breaker and the Square D breaker above it as the width of the raised part is the full width of the breaker, unlike the other Square D breakers.
See what I am referring to?
08-11-2009, 09:47 AM #9
Re: Loose breaker
I don't know, Jerry. I was thinking the same thing, but look at this:
HomeLine ® Circuit Breakers - Schneider Electric United States
I would tend to agree that it is either improperly installed, or not made for the panel it is installed in. This may be due to the breaker being a mini or tandem.
Randall Aldering GHI BAOM MSM
Housesmithe Inspection
www.housesmithe.com
08-11-2009, 09:52 AM #10
Re: Loose breaker
This will save looking it up on the web site.
www.housesmithe.com
08-11-2009, 10:05 AM #11
08-11-2009, 10:14 AM #12
Re: Loose breaker
square D Homeline breaker in a Square D QO panel
08-11-2009, 10:20 AM #13
08-11-2009, 01:46 PM #14
Re: Loose breaker
my bad !
I guess thats what I get for looking at it with that stupid laptop instead of my desktop
08-11-2009, 01:54 PM #15
Re: Loose breaker