Results 1 to 9 of 9
    Ryan Stouffer's Avatar
    Ryan Stouffer Guest
    Default Service entrance ground wire
    There are two 70 amp. services coming into this service box but only one ground wire is that acceptable.
    Default Re: Service entrance ground wire
    Quote Originally Posted by Ryan Stouffer View Post
    Ryan,
    I don't think you can really call them mains, since main refers to one, but I am at a loss as to what to call it.
    The single ground is fine.
    You probably noticed that the doubled neutral conductors in pic #4 are not. Each conductor should have it's own terminal.
    Apr 2009
    NY State
    Actually Gunnar, there can be up to SIX "mains".
    Those are both "main disconnects" or "service disconnects".
    Apr 2009
    NY State
    Exactly.
    What's crazy is that there is an empty lug right there.
    "two ... services coming into" or do you mean 'two feeders going out from' that service equipment?
    I see the meter right there to the right, which likely means there are bus bars feeding those two mains, which are feeding (i.e., 'have feeders' going out to panels).
    On the open lug and double tapped neutrals I am going to guess that who ever wired that up (most likely an electrician as that is service equipment) looked at the larger neutral terminal lug and the smaller ground terminal lugs and thought to themselves ... 'Hmmmm ... I have 3 ground wires and 2 neutral wires but only 1 neutral terminal.', not realizing that at service equipment they are all basically both.
    Quote Originally Posted by Speedy Petey View Post
    Well, that is good to know. I have never know what to call it when there are multiple mains.
    Gunnar,
    You know what to call it ... you just did: "multiple mains".
    Those multiple mains, however, cannot be added up to determine a service size.
    Gunnar,
    Of course not. They are "multiple mains", so you multiply! Right?
    Apr 2009
    NY State