Results 1 to 30 of 30
Thread: Power strips for kitchen outlets
09-21-2009, 09:57 AM #1
This is new construction so apparently the AHJ was okay with but I've never seen this before. There are no standard kitchen counter top outlets. Instead, there are power strips secured against the underside of the cabinets (yes, they are GFI protected). Any comments?
09-21-2009, 09:58 AM #2
09-21-2009, 10:12 AM #3
Re: Power strips for kitchen outlets
They may be too high above the countertop.
Are they less than 20" above the countertop?
Most cabinets are set at 18" above the countertop, some slightly higher.
09-21-2009, 10:22 AM #4
Thanks JP.... they're exactly 18" above the surface. I was more thinking about the amount amount of wattage going through them. I the strips rated for that?
09-21-2009, 11:05 AM #5
Matt,
You won't get any more wattage through them than the 20 amp circuit will carry.
Just make sure those assemblies are rated for 20 amps, that would be the main thing.
Those are made in two types, with a cord and plug and without a cord and plug for being permanently wired in. Those should be the ones made without the cord and plug, and would need to be rated for 20 amps.
09-21-2009, 11:07 AM #6
09-21-2009, 11:11 AM #7
http://www.wiremold.com/shared_content/pdf/ed497.pdf
http://www.wiremold.com/shared_content/pdf/ed1412.pdf
15 amp rated receptacles on #12 AWG 20 amp rated circuit conductors, suitable for use on 20 amp circuits with multiple outlets (which they are).
09-21-2009, 11:12 AM #8
I am more interested in those lights and how they are wired, especially with those exposed wires.
Are they cord and plug connected with the plugs cut off, are they cord and plug connected and plugged into those outlet strips with their wires secured in place (making them improper), or are they ???
09-21-2009, 11:46 AM #9
09-21-2009, 12:05 PM #10
09-21-2009, 12:17 PM #11
Here are some 120 volts ones: http://www.americanlighting.com/LVPX_ALLVP.pdf
Note that the bottom of the cabinet must be:
"Mount at the top of cabinets or under cabinets or any horizontal surface that is at least 5/8” thick."
And that they be spaced at least:
"Install linked units with 12" or 24" extension cords with at least 12" spacing between units in well ventilated areas."
09-21-2009, 01:22 PM #12
They are Plugmold. Made by wiremold.
Which is a surface mounted raceway.
Which is perfectly legal way to place the outlets provide they meet the required measurements Jerry spoke of.
There is no code that requires the outlets to be in the wall over the counter,
09-21-2009, 04:36 PM #13
OK, side question. What was the counter top made of? If granite did ya do a radon test? Just getting into this, an awful, awful lot to learn.
09-21-2009, 04:38 PM #14
Are any home inspectors recommending or performing radon tests on granite countertops?
09-21-2009, 05:01 PM #15
Oh NO!
Not this topic again!
Many will say no, some will say yes, others will ask why.
Do you recommend a radon test whenever there is a natural stone floor in the house?
How about when there is granite around the tub or shower?
09-21-2009, 05:13 PM #16
Well, here we are, got a awful, awful lot to learn. Good thing I am in the right place to get the "real" info on all of this.
09-21-2009, 05:18 PM #17
09-21-2009, 05:19 PM #18
09-21-2009, 05:22 PM #19
09-21-2009, 05:23 PM #20
If they are low voltage what's the problem. Even if they are line voltage and terminated properly.
The wire CAN be exposed. I would hardly call that subject to physical damage.
I will say. I HATE those line voltage kits. They make it seem so easy to install them, when it is near impossible to do legally.
09-21-2009, 05:23 PM #21
09-21-2009, 05:34 PM #22
09-22-2009, 04:42 AM #23
" Not this topic again! "
OK Jerry
Your choice, Religion, Radon, or Mold.
Whats it gonna be boy?
09-22-2009, 09:37 AM #24
09-22-2009, 11:05 AM #25
OK, got it everybody. Went back and searched the old threads.
09-23-2009, 02:30 PM #26
09-23-2009, 02:34 PM #27
Joe,
When there is one receptacle on one circuit, the the receptacle is required to be rated at least as high as the circuit overcurrent protection (to limit the receptacle from burning up from being rated lower than what the trip point of the overcurrent device is).
When there is more than one receptacle on a circuit, the circuit overcurrent protection device is to protect the circuit conductors, and it is unlikely that the circuit will be overloaded by one appliance plugged into one receptacle, which means the most common scenario would be two or more appliances plugged in and overloading the circuit and tripping the overcurrent device, thus each one can be 15 amps instead of being required to be 20 amps.
09-23-2009, 02:40 PM #28
Thanks...My curiosity has been satisfied.
I guess if I would of looked at my kitchen outlets and saw that they were 15A outlets / 12 AWG wire on a 20A breaker I wouldn't have been so curious.
09-23-2009, 04:13 PM #29
09-24-2009, 04:59 AM #30
"You forgot politics "
Not politics, just Bush