Results 1 to 11 of 11
Thread: Unconventional ground clamp
10-02-2009, 08:32 PM #1
The grounds are tucked out through a cable clamp. Is it wrong? Yes. How wrong is it?
The tie-bar for two breakers is a galvanized nail. The breakers don't match, one is 15A the other is 20A, feeding a baseboard heater. Is it a hazard?
The third beef is I couldn't view the main fuses, unable to open the door on the main disconnect panel.
10-02-2009, 08:46 PM #2
Re: Unconventional ground clamp
John,
It seems to me that the cable clamp is just that... a cable clamp. Not a grounding terminal.
10-02-2009, 09:15 PM #3
10-02-2009, 09:20 PM #4
10-03-2009, 07:09 PM #5
I've heard debate over this but - as far as I know, any splicing of the grounding conductor must be irreversible.
10-03-2009, 09:26 PM #6
10-05-2009, 12:49 PM #7
10-05-2009, 12:52 PM #8
John,
A split bolt is for 2 conductors, not a bunch of grounding conductors. The proper method would be to install an auxillary ground buss and terminate them there.
10-05-2009, 02:35 PM #9
10-05-2009, 04:22 PM #10
How about running your ground wire to the hot water pipe coming out of the water heater.
10-05-2009, 05:12 PM #11