What is the NEC requirement for open bulbs in shower/steam showers?
12-05-2009, 02:01 PM #2
Re: Light fixtures in showers
NEC 410.4 .........shall be installed so that water cannot enter or accumulate in wiring compartments,........
12-05-2009, 02:20 PM #3
The trim must be Damp Location rated and the bulb needs to be listed as acceptable with that trim. There are open trims that will meet this requirement.
12-05-2009, 02:45 PM #4
(A) Wet and Damp Locations. Luminaires installed in wet or damp locations shall be installed such that water cannot enter or accumulate in wiring compartments, lampholders, or other electrical parts. All luminaires installed in wet locations shall be marked, “Suitable for Wet Locations.” All luminaires installed in damp locations shall be marked “Suitable for Wet Locations” or “Suitable for Damp Locations.”
That means UL listed for damp locations.
Additionally, some manufacturers require GFCI protection for luminaires installed in shower stalls and over tubs.
http://www.us.kohler.com/onlinecatal.../1015878_4.pdf
12-05-2009, 03:29 PM #5
I am of the opinion that a steam shower zone or sauna zone is by its very nature a wet location under the NEC. Thought I'd say that first, since you asked about steam shower and open lamp fixture.
It depends. Height of that ceiling, relationship to the floor of the bathroom as well as the floor drain of the shower, and the height of the shower threshold or bathtub rim. Depends on if that fixture is subject to shower spray (mounted shower head movable or shower wand). Steam and jet showers little more dicey depending on height from shower threshold floor esp. if lower alcove. Condensation collection in the lamp holder often of issue even if not subject to spray can require wet zone and lense for safety. GFCI protection depending on height and accessibility from floor and if not non-conductive trim & lense if its too close (short height tiled ceiling over shower) - if having to be in the "wet zone" to service/change lamp and ceiling height less than 7 feet above shower threshold floor probably should be wet indoor fixture non conductive trim & lense and GFCI protected esp in STEAM shower for safety.
2008 NEC you'll find general references 410.10 (A) & 410.10 (D). 2005 NEC 410.4 (A) and 410.4 (D). Definitions of Locations, Dry; Locations, Damp; and Locations, Wet are found in General Definitions in the 100 area.
Remember that by the nature of the thing - tiled showers are washed walls. Tough to judge height when walls are tiled to ceiling and ceiling is tiled - usually that's an indication that condensation collects regularly on the ceiling (steam shower right) during regular use and/or water spray even if indirectly from bouncing off the user's body hits that ceiling - perhaps due to short clearance or by the nature of the thing, thus a wet zone not just a damp one; although it could be a decorating decision on a non-steam shower with a fixed non-adjustable shower head with plenty of clearance - can't tell from the picture.
Finally - check the listing and labeling for the lamp itself - some packaging will state damp or wet location use - only when protected from direct contact or requiring a lense, guard or cover - ex. any liquid water coming into contact with the hot lamp itself while in use may cause it to shatter - thus endangering the party in the shower with a "rain" of glass shards. (similar to luminaires in clothes closets - more than one reason to require guard).
12-05-2009, 04:04 PM #6
12-05-2009, 05:31 PM #7
I ran into a question like that a few weeks back.
On the manufacturer site is this statement.......All trims are suitable for damp locations; only shower trims are listed for wet locations.
Notice inside it says damp location.
I called this out and the developer reordered a glass trim to replace the one I removed in the picture.
You want those bulbs covered if within 3 feet of the tub/shower and less than 8 feet up from where your feet stand.
12-05-2009, 07:54 PM #8
This is fine, but it is not always required. See post #3.
An open recessed light is perfectly complaint over most "typical" standard showers/tubs, although this is rarely seen.
IF the light is subject to shower spray then it MUST be wet location rated.
I am also of the opinion that if this is a true sealed steam shower then to me that would create a condition allowing water to collect due to the extreme moisture. Sure, a really hot shower would be similar, but nowhere near the intensity of a closed steam shower.
12-05-2009, 08:05 PM #9
Hi Speedy
We miss you at NACHI and Nick nominated you to post directly.
Back to subject I would always like to see a cover over the bulb as people might put the wrong one in ,like say an incandescent that will shatter and spray glass all over you while naked.
Yes nanny subject ,but people can be stupid or not know any better.
I was happy to see the developer took my advice on the final walkthough the other day.
12-05-2009, 08:50 PM #10
????? - You have to be "nominated" to post on the board. What's up with that? I don't follow the "pissing matches" too closely but it's funny there's a restriction to posting when the word on the street is that there's pretty much none to being a master, grand poo-bah inspector.
12-05-2009, 09:04 PM #11
Slow down on what ever you are smoking ,as this is a systems thread.
Please take your rhetoric to an appropriate thread,or are you a troll.?
Would you like to show off your Inspection skills and add something that actually helps Richard here?
Thank you
My email is listed and you can PM if you have some personal demon that needs a rage outlet.
12-05-2009, 09:10 PM #12
12-05-2009, 10:40 PM #13
12-05-2009, 10:55 PM #14
Apparently I've gotten gun shy and/or wordy.
When I checked back to read the updates on this topic thread, an Inter-Nachi banner ad appeared. This is a shower/steam shower thread and I feel so dirty (I need a shower now!)
Guess that means that someone has agreed to PAY B.H. for advertising.
12-05-2009, 11:01 PM #15
"The goal of Hann Tech Marketing Links / InspectionNews is to have peaceful, educational and informative discussions related to the inspection business. Please discuss the topics and do not get into personality conflicts and/or arguments.
12-05-2009, 11:23 PM #16
www.inspectaz.com
12-06-2009, 06:57 AM #17
BE: BH (aka the Hann) is a nice guy, sometimes, but has an appalling lack of understanding of the definition of "arguments", as apparently do you. If you own a dictionary, please peruse the two terms "discussion" and "argument", all the while juxtaposing the nuances of their meanings. Come back to us when your finished for your next assignment.
12-06-2009, 09:38 AM #18
Well I did not have to look up discussion or argument, but I did have to look up "juxtaposing"
So for others (if any) who might not know the meaning.
juxtaposing: to place close together or side by side, esp. for comparison or contrast.
Arron, you must be Bill O'Reillly fan, you know the word of the day thing he does .
12-06-2009, 09:53 AM #19
12-06-2009, 10:17 AM #20
12-06-2009, 07:47 PM #21
12-06-2009, 08:34 PM #22
12-07-2009, 07:11 AM #23