Results 1 to 17 of 17
02-27-2010, 09:32 PM #1
Sizing bonding jumper at water meter
Is there a straight forward rule for sizing the bonding jumper at a water meter - all I can find is per table" 250.66"... which I cannot seem to find online.
- Thanks
02-27-2010, 10:01 PM #2
Re: Sizing bonding jumper at water meter
At least a #6 copper.
02-28-2010, 07:40 AM #3
Is this what you wanted?
02-28-2010, 10:41 AM #4
NFPA 70: National Electrical CodeĀ®
This is a link to the 2008 NEC on the NFPA website.
It is a Read Only PDF. You will need to register in order to see it.
But it's better then nothing at all
Scroll down to where it says " view the document online"
02-28-2010, 11:53 AM #5
Thanks to all - I was trying to imagine a "logical" reason why this was attempted on a system with AWG 3 copper service entrance conductors:
02-28-2010, 12:34 PM #6
02-28-2010, 01:50 PM #7
Because it is a legal install.
Table 250.66 states that #2 or smaller copper you use a # 8 copper for the jumper.
#3 copper is smaller then #2 copper.
Wire sizes up to #1 ---> The SMALLER the number the LARGER the wire.
(Just like #14 is smaller then #12)
It is this way until you get to 1/0. Then you go 1/0,2/0,3/0,4/0, 250,300,350,400,500 ......
02-28-2010, 02:44 PM #8
The size is correct however the installation is incorrect. The second, unnecessary wire, appears to be between the ground connector and pipe. As you can see by the corrosion it will reduce the effectiveness of the correct ground wire.
02-28-2010, 02:53 PM #9
I don't know that the second wire is unnecessary ... but I expected Ken H. to have mentioned that it was improperly installed instead of "Because it is a legal install."
That is a pipe grounding clamp with a terminal for the grounding conductor, the clamp clamps onto the pipe, then the conductor goes into the terminal.
The corrosion looks like it is because of dissimilar metals: the clamp is dissimilar from the pipe - notice the brass/bronze clamp just above it on the copper pipe with no corrosion, versus this clamp being steel and having corrosion.As you can see by the corrosion it will reduce the effectiveness of the correct ground wire.
02-28-2010, 02:54 PM #10
Sorry the picture was unclear, those jumpers are 8 AWG, so why is the second (unnecessary and incorrectly installed) jumper there?
(Other than "All two-six-pack installations shall be provided with two jumpers, as specified in table 350.266, if you see double when you look in the book..." ).
I know given the the way its cobbled up its probably just a failure of the Bozone Layer. But when I see something like that, I just cannot stop myself from asking "is there a possible why?"
02-28-2010, 04:43 PM #11
02-28-2010, 04:54 PM #12
I was waiting for other replies to assess what was asked and and what was shown, and I know how you used to (not as much now) try to pick responses apart, (others did to, and are also much better at controlling themselves too
), so I expected your post to be spot on as you seem to enjoy doing such things and lo-and-behold I was ... disappointed.
Sorry, could not resist either.
Usually, the question is answered and then we continue to point out other things which are wrong - and that is a GOOD THING as that helps all learn without having to ask questions one does not even know to ask.
Keep up your part of the picking apart, we ALL learn from each other doing that.
02-28-2010, 05:31 PM #13
I have no problem at all with people expanding the scope of their answer to any question I ask - the most dangerous questions in this business are the ones you don't even know you're suppose to be asking.
That's why I ask questions like that one: one look at the workmanship and you know that whoever installed that jumper not have to have a "reason" for anything they did, I just wanted to know if there was any conceivable reason I had not considered why it would be reasonable to double-jumper (assuming it was done correctly) such a bond.
(And while you all were at it, I was a bit surprised that no one mentioned the lead supply line.)
02-28-2010, 05:45 PM #14
03-01-2010, 03:46 AM #15
By the way, here it is only the end of February, and I think I've already seen my "roof of the year" at this same property...
03-02-2010, 06:44 AM #16
Table 250.66 givers the proper size bonding wire to be used.
It is based on service conductor size.
04-26-2010, 06:47 PM #17
Well we are on the subject of bonding, grounding, and the aggressively stupid things people do:
From this morning's foreclosure: