    I inspected a townhouse the other day and located a SQD subpanel behind the door in the hall bathroom. The townhome was built in 1995. I understand NEC does not permit service panels in bathrooms. Was this particular code written after 1995? Building is located in Pacifica, California.
    Default Re: Subpanel in bathroom
    Let the Electrical Contractor determine its new location when he replaces it since it is contaminated with paint overspray.
    georgia
    overcurrent protection is not allowed in a bathroom that being said no panel or service eqipment is allowed in a bathroom.
    Default Re: panel in bathroom
    The 1996 NEC is the oldest I have on my computer (and was too lazy to look back at my books) and ... the 1996 NEC did not allow overcurrent devices to be installed in bathrooms, and it was not marked or indicated that it was a new limitation.
    - 240-24. Location in or on Premises.
    - - (e) Not Located in Bathrooms. In dwelling units and guest rooms of hotels and motels, overcurrent devices, other than supplementary overcurrent protection, shall not be located in bathrooms as defined in Article 100.
    Dec 2007
    Chico,Ca
    That panel is a obsolete SQ D Trillaint loadcenter & the box is all plastic, I fail to see the "paint overspray".
    The code section 240-24(e) 1st appeared in the 1993 NEC & since CA has been slow to adopt newer editions it prob. complied with the code in effect at the time of the permit being issued.
    Richard Stanley's Avatar
    Richard Stanley Guest
    Looks like paint to me also.
    chris mcintyre's Avatar
    chris mcintyre Guest
    ... I fail to see the "paint overspray".
    If you zoom in a few times (Ctrl, +,+,+) you can clearly see the over spray on all of the conductors.
    Rollie,
    How many "white" Square D breakers have you ever come across?
    dana1028's Avatar
    dana1028 Guest
    ditto - the 'no panels in bathrooms' appeared in the 1993 NEC and did not get adopted in CA till 1996 - so the panel in the bathroom would have been approved at that time.
    As Rick has pointed out, the panel appears to be damaged from over spray.
    This situation is a toss up - some jurisdictions will make you move the panel now that it has to be replaced, others will let you replace it where it is - rational being a replaced panel does not make the situation any less safe than it was before.
    That said, South San Francisco [location of original poster] will let you replace the panel at the same location.
    On The Mason-Dixon Line
    Rick-
    Rollie stated that it is an OBSOLETE Square D Trillaint loadcenter.
    Those breakers were white and that's what is pictured in the original post.
    Google Square D Trillaint breakers. There are some available on Ebay
    I did see overspray on the Conductors. Not so much on the loadcenter.
    If it's the conductors, changing the loadcenter will do absolutely zero as the overspray will still be there.
    Dec 2007
    Chico,Ca
    The one & only reason to replace the panel is it's obsolete & the breakers are hard to get, which means expensive. The panel complies w/ the code in effect in the time of installation so it's fine.
    "...a SQD subpanel behind the door in the hall bathroom"
    BEHIND THE DOOR!!?
    BEHIND THE DOOR!!?
    I t-o-l-d y-o-u g-u-y-s we'd have problems if we kept insisting that a door was an obstacle to a light switch ... ... here we go again with those stupid doors ...
    dana1028's Avatar
    dana1028 Guest
    BEHIND THE DOOR!!?
    And your point is?
    "And your point is?"
    No point, just subtle humor, in referance to the thread.
    http://www.inspectionnews.net/home_i...ht-switch.html
    I had a similar referance to the same thread when I asked, "Where's the door?".
    Does that help?
    Atlanta, Georgia
    JP, I can't believe you let the magic phrase go by without a comment about underwater boats. You must be mellowing.
    Kevin Strauss's Avatar
    Kevin Strauss Guest
    As this home was built in 1995, the 1993 NEC would apply, unless it hadn't yet been adopted by the locality. NEC 1993, Section 230-70(a) concludes, "Service disconnecting means shall not be installed in bathrooms".
    As you have stated, and the photograph clearly shows, this is a sub-panel. The service disconnecting means are clearly somewhere else.
    Therefore, while placing a subpanel in a bathroom just doesn't sound "right", there is actually nothing wrong with the location of the installation. The contamination of the panel and its contents is another matter, though.
    (This question, or something quite similar frequently shows up on the New Jersey license exam.)
    Dec 2007
    Chico,Ca
    Quote Originally Posted by Kevin Strauss View Post
    The 1993 NEC is irrelevent, it was not adopted in 1995 in California what is relevent is the NEC adopted at the time of the permit being issued, and that would be 1990 or earlier and the panel is compliant with the code in effect at the time. The NEC or other codes are not retroactive otherwise we would be demoing all structures every 3 years, if the panel is replaced then the issue of it being in a residential bathroom is going to be a major problem, it is wee weeing about nothing.
    Kevin Strauss Guest
    Then it appears that we agree. While abhorrent, the presence of this sub panel in a bathroom in and of itself does not constitute a violation of whatever code was in effect at the time. Now, about all that paint!!
    The NEC code (as taken from the IRC) states in E3304.6 Integrity of electrical equipment.
    Internal parts of electrical equipment, including bus bars, wiring terminals, insulators and other surfaces, shall not be damaged or contaminated by foreign materials such as paint, plaster, cleaners or abrasives, and corrosive residues. There shall not be any damaged parts that might adversely affect safe operation or mechanical strength of the equipment such as parts that are broken; bent; cut; deteriorated by corrosion, chemical action, or overheating. Foreign debris shall be removed from equipment.
    Dec 2007
    Chico,Ca
    There is some overspray on the conductors, big deal & no reason to whine about it, if it was all over the bus would have a different opinion but it's a white PLASTIC box & interior.
    Roger Frazee's Avatar
    Roger Frazee Guest
    Heres a trilliant panel to compare.
    These were really pretty nice panels and had some very good features but square d wanted a fortune for them and they just were to darn costly. My understanding was the breaker internals were QO (you can see the trip windows in the picture). Anyway in Europe their load centers called 'consumer units' have been non metallic plastic for many years. and are similar to the trilliant in some respects. I also think it is possible that the bus stabs in the unoccupied spaces may be contaminated with paint spray.
    That being said I have never had an inspector make me replace a load center for paint spray like we see in this panel posted by Steven.
    I will say that the painter and I would have had some serious words if he did that to a panel of mine ...he can either cover it or have me cover it. They know not to spray the interior of a panel yet it happens all the time.....
    STEVEN CHUNG Guest
    Thanks everyone...your input was definitely helpful. I did note the overspray and I recommended to have the panel evaluated by an electrician.
    Bruce,
    I let if go by as I figured he was playing with it in the bathtub and did not pick it up after the bath, so his mother hid it behind the door.
    You did notice that I changed to title in my posts, right?
    Roger Frazee Guest
    Bruce,
    Generally speaking this is what a feeder to a sub-panel looks like ...
    Jerry's refernce to a panel in a submarine as a sub panel is also INCORRECT. There is a correct and proper term for that type of panel.
    How bout it Jerr ?