    Jon mackay's Avatar
    Jon mackay Guest
    Default exposed cable run
    Is extra protection required here?
    Ron Bibler's Avatar
    Ron Bibler Guest
    Default Re: exposed cable run
    Nice hand rail... They should have ran it with the stairs
    Best
    Ron
    Apr 2007
    state of jefferson
    Quote Originally Posted by Jon mackay View Post
    no! just your usual protection
    JD Weekley's Avatar
    JD Weekley Guest
    Well, I don't think that's Mike Holmes approved....
    Nampa, Idaho
    The cable should be repalced with conduit or re-routed through wall cavity.
    Aug 2008
    334.15 Exposed Work.
    In exposed work, except as provided
    in 300.11(A), the cable shall be installed as speci
    fied
    in 334.15(A) through (C).
    (A) To Follow Surface.
    The cable shall closely follow the
    surface of the building
    finish or of running boards.
    (B) Protection from Physical Damage.
    The cable shall be
    protected from physical damage where necessary by rigid
    metal conduit, intermediate metal conduit, electrical metallic
    tubing, Schedule 80 PVC rigid nonmetallic conduit, or
    other approved means. Where passing through a
    floor, the
    cable shall be enclosed in rigid metal conduit, intermediate
    metal conduit, electrical metallic tubing, Schedule 80 PVC
    rigid nonmetallic conduit, or other approved means extending
    at least 150 mm (6 in.) above the
    floor.
    Looks like (A) has been followed. Physical protection is a judgement call, but, IMO the cable could be possibly damaged by a vacuum.
    Anywhere a dog can chew on it should have protection.
    But like Jim says, it's a judgement call and the code leaves it up to "where necessary".
    Feb 2010
    Omaha
    it there to hang socks for drying