Thread: No main handle
    May 2008
    N. Syracuse, NY
    Default No main handle
    Pending sale on this house was thwarted by the discovery of service equipment with main lugs only. Someone inserted old 60 amp entrance cable into a new 150 amp main lug panel. My question is does the entire panel have to be changed out, or is it ok to back feed a 60 amp breaker with the SEU? Thanks for prompt, thoughtful replies only.
    Aug 2008
    Default Re: No main handle
    If you can get a listed hold-down bracket and it can be used in that panel, you could install the 60 and backfeed the panel. Some hold-downs are not for use with all panels. Square D has one that is only for the smaller panels.
    Quote Originally Posted by Mike Locurcio View Post
    Are you saying that the home only has a 60amp service? If that is the case that could also be a problem as most insurance providers will no longer cover a home if it has only a 60 amp service.
    May 2008
    N. Syracuse, NY
    Thank you gentlemen for prompt, courteous replies. Further investigation reveals that this Square D panel allows for conversion to a main breaker by simply removing the lugs and bolting to the bus bars. This still leaves the problem of the 60 amp entrance cable as you pointed out, Scott. I am recommending a wire upgrade be performed at the same time.
    Mar 2009
    Colorado Front Range
    Needy bastard, huh?
    Probably just doesn't like our nice friendly chit chats