Results 1 to 17 of 17
Thread: Weather Head
    Erwin, TN
    Default Weather Head
    Does anyone else think this should be a defect. Notice the wood holding the wires up.. SEE PICTURE
    Default Re: Weather Head
    Yes, it is a defect. If the extra height is needed, a taller mast needs to be installed. $$$
    The real problem there is that the building is laying on its side. Just how do you get in the front door?
    Egbert Jager
    Diamond Home Inspection
    http://www.diamondhomeinspection.ca
    Sep 2009
    Twin Cities, Minnesota
    Gunnar -- I was thinking the same thing. They might be better off replacing those shingles with some vinyl siding!
    -Jon
    Errickson Home Inspections, LLC
    http://www.erricksonhomeinspections.com
    Bob Winchester's Avatar
    Bob Winchester Guest
    The utility did not approach the service mast at the correct angle to comply with any code. The mast was not constructed tall enough to approach from this angle. Normally the utility will just connect it but maybe they requried the wood support to be installed. They could terminate at the support and keep the wiring at the proper height above the roof overhang and be code compliant. Nothing says the service lateral must terminate at the mast. There is no problem terminating to the structure. It certainly does look hokey.
    Mar 2008
    Charlotte NC
    Gunner, the house is built on the side of a moutain!
    James Duffin's Avatar
    James Duffin Guest
    It appears that the only thing amiss with the installation is that there is not 18" of clearance as required in Exception 3 shown below. (Not sure what going on with the flashing)
    230.24 Clearances.
    Service-drop conductors shall not be
    readily accessible and shall comply with 230.24(A) through
    (D) for services not over 600 volts, nominal.
    (A) Above Roofs.
    Conductors shall have a vertical clearance
    of not less than 2.5 m (8 ft) above the roof surface.
    The vertical clearance above the roof level shall be
    maintained for a distance of not less than 900 mm (3 ft)
    in all directions from the edge of the roof.
    Exception No. 1: The area above a roof surface subject to
    pedestrian or vehicular traffıc shall have a vertical clearance
    from the roof surface in accordance with the clearance
    requirements of 230.24(B).
    Exception No. 2: Where the voltage between conductors
    does not exceed 300 and the roof has a slope of 100 mm in
    300 mm (4 in. in 12 in.) or greater, a reduction in clearance
    to 900 mm (3 ft) shall be permitted.
    Exception No. 3: Where the voltage between conductors
    does not exceed 300, a reduction in clearance above only
    the overhanging portion of the roof to not less than 450 mm
    (18 in.) shall be permitted if (1) not more than 1.8 m (6 ft)
    of service-drop conductors, 1.2 m (4 ft) horizontally, pass
    above the roof overhang, and (2) they are terminated at a
    through-the-roof raceway or approved support.
    FPN: See 230.28 for mast supports.
    Exception No. 4: The requirement for maintaining the vertical
    clearance 900 mm (3 ft) from the edge of the roof shall
    not apply to the final conductor span where the service
    drop is attached to the side of a building.
    Fuquay Varina, NC
    Whats the abandoned conduit at the base of the mast too? It doesn't look kosher left with conductors hanging out of it.
    Mike Schulz License 393
    Affordable Home Inspections
    www.houseinspections.com
    Actually, it's OK if you use a special clamp that can be found in the better supply houses.
    Thanks Eric and James.
    "Approved support" can mean many things to many people,apparently.
    The insulation is prone to chafing in that picture. I would still call it out, even if the height was correct.
    The clamp would prevent chafing of the insulation. But why not just put up a proper 4X4 mast with an insulated knob?
    Even with the clamp, a lousy 2X4 scabbed to the side of the shack would not be permitted where I live.
    Mike, you are right, those extra feeders don't look kosher at all, kind of like someone was bypassing the meter there. Why do that?
    John & anyone else,
    If you took my comment seriously - don't.
    John & anyone else,
    Thanks Eric. It looked serious to me. Scary, in fact.
    Erwin, TN
    The extra wires at bottom werr not hot.. Good Eye
    Several things wrong in that photo, and some potential things if other unknowns are present.
    Not properly flashed is one thing wrong.
    Not at lest 18" above the overhang, provided that is indeed a gable overhang of that much (approximately 2-1/2 feet of overhang at the gable).
    If not over an overhang, then the 18" goes out the window and you either have 3 feet minimum clearance for 4/12 and greater slopes or 8 feet minimum clearance for under 4/12 slopes to flat roofs.
    Also, if that is an overhang, then the maximum distance across the overhang is 4 feet, and the maximum conductor length is 6-1/2 feet (to allow for the upward slope extra length).
    Even if abandoned (and just because there is no power does not mean it is abandoned) - that conduit fitting needs to end in a junction box with those wires properly capped off in the junction box.
    That board has to go.
    Those are for starters, ... only then should we start to deal with the sideways house ...
    Sep 2008
    Texas
    The original picture was giving me a creek...crek...creik....making my neck hurt.
    Denny Waters's Avatar
    Denny Waters Guest
    Copper neutral equals stretch.