    Default painted panel
    OREP Insurance
    Richard Rushing's Avatar
    Richard Rushing Guest
    Default Re: painted panel
    NOpe. If you can see paint on the buss bars and on the breakers... much different deal.
    As is... I wouldn't
    Rich
    Houston, Texas
    I agree with Richard. As professionals, we have to be able to draw a line somewhere between the rigid letter of the code and its practical intent.
    The few paint speckles shown in your photo on the panel shell are of no consequence in the grand scheme of things in my opinion. However, paint contamination on conductive or heat dissipating surfaces of bus bars, breakers, and wire terminals would be a different matter.
    Also in agreement. That little bit, and not on anything of consequence, is not a problem.
    Oct 2003
    Rockwall Texas
    Dan,
    You'll probably get a call in a few years when your buyer decides to sell that house and a new inspector comes out and tells his client that the panel is contaminated and should be replaced at a cost of 3 grand. He'll be wanting a check from you.
    It happens trust me.
    Still, I wouldn't call it out as the other seasoned HI's mentioned.
    Oregon
    Or how about some drywall mud? This one I did call out because it is actually on the connection points. It has to be quite a bit more severe than the picture you posted for me to mention it.
    Replace those breakers.
    Agreed-- just those breakers... not the whole panel.