Thread: Bootlegged Main
08-22-2010, 04:56 AM #1
Bootlegged Main
The main breaker on this 200A panel is not connected. The panel is fed through a separate 100 A breaker on side bus. (see pictures).
The cover is labeled - "Not the main switch" and "main switch".
Is this against any code?
It looks like a jury rig to me, but does the labeling make it ok?
Also, I don't often see distribution breakers direcftly oposite the main breaker as it is usually lugged in place and doesn't allow space?
08-22-2010, 06:53 AM #2
Re: Bootlegged Main
This looks like it was done because more breaker spaces were needed than a standard 100 amp panel could provide. This might be fine. The big consideration is if the breaker hold-down clip or bracket was used and if it can be used in that panel.
08-22-2010, 09:51 AM #3
Re: Bootlegged Main
08-22-2010, 01:38 PM #4
Re: Bootlegged Main
Originally Posted by Jerry Peck
08-22-2010, 01:52 PM #5
Re: Bootlegged Main
08-22-2010, 09:49 PM #6
Re: Bootlegged Main
Ken,
- The back feed 100 amp breaker would probably be ok if this were not a main circuit breaker load center, as such there will be no provision for installing the factory back feed main circuit breaker retaining clip.
- The service feeders enter the load center enclosure via an unprotected knockout. There is no conduit, connector, locknut or bushing to protect the # 4 AWG or larger conductors.
- The duct tape is not a legitimate knockout closure plug, aka push penny or Hoffman plug.
- The type AC cable does not terminate in armor clad connectors.
- There appears to be a white neutral on the ground bus located in the bottom of the panel.
- That is about all I see from you pix…