Results 1 to 19 of 19
Thread: Is this okay?
09-30-2010, 02:02 PM #1
09-30-2010, 02:43 PM #2
Re: Is this okay?
It looks OK to me except there should be a interlock so the door can not be opened when the lever is in the on position. That appears to not be working since the door is open in the on position.
09-30-2010, 03:06 PM #3
Re: Is this okay?
Hey at least your had fuses.
09-30-2010, 04:04 PM #4
Re: Is this okay?
I don't see where the ground and neutral are terminated to the enclosure, likely leaving the enclosure not grounded.
09-30-2010, 08:16 PM #5
Re: Is this okay?
09-30-2010, 10:10 PM #6
10-01-2010, 06:39 AM #7
Re: Is this okay?
Rick,
If you return to this thread would you please send me the pic for your post? I would like a larger file for a presentation at my local chapter. Thanks in advance.
10-01-2010, 07:41 AM #8
Re: Is this okay?
Hey Jerry,
The ground and neutral are terminated behind the fiberboard insulator located in the lower left side of the disconnect. Unfortunately you can't tell from the picture if the neutral (grounded conductor) bonding screw was installed and thus potentially ungrounded as you stipulated.
I also do not see any form of oxide inhibitor as is almost always required by the wiring manufacturer of all aluminum cables at termination points and therefore code mandated per "NFPA 70 2008 NEC Art 110.3(B)" and previous editions.
Cordially,
Bill Nolte, C.S.H.O.
Master Electrician
Fort Worth, Texas
10-01-2010, 01:40 PM #9
10-01-2010, 02:11 PM #10
Re: Is this okay?
Copper pipe instead of fuses
10-01-2010, 05:44 PM #11
Re: Is this okay?
10-01-2010, 05:48 PM #12
Re: Is this okay?
Manufacturers do not "require" anti-oxidant to be use, therefore it is not a violation of 110.3(B).
"Should" anti-oxidant be used? Sure, it cannot hurt and typically helps.
Now, do not take "should" as past tense of "shall", take "should" as meaning "it is a good idea".
10-01-2010, 08:01 PM #13
Re: Is this okay?
Not all, but several wire and cable manufacturers do require use of anti-oxidant compounds on their aluminum cable at terminations. You need to read the manufacturers literature that should be requested with cable deliveries similar to MSDS sheets for chemicals. Some are automatically forwarded and some must be requested. However as stated code mandates compliance with manufacturer instructions.
I Direct you to the following link and suggest you read under Corrosion Resistance where you will find the following;
"Corrosion Resistance
The inherent corrosion-resistance of aluminum is due
to the thin, tough oxide coating that forms instantly
when a fresh surface of metallic aluminum is exposed
to air. This type of oxide is particularly resistant to most
types of corrosion. The ability of aluminum to
withstand harsh environments is responsible for its
widespread use in trays and conduit for electrical cable
as well as many industrial components and vessels.
When corrosion has appeared, it is usually related to
connections between dissimilar metals in the presence of
moisture – protective measures such as a grease, antioxidant
or protective coating should be used to prevent
these occurrences. Environments that do tend to be
aggressive to aluminum include alkaline soils and some
types of acids. This means that buried aluminum
conductors should be protected from corrosion by
insulation or an extruded covering. In sulfur-bearing
environments, aluminum performs much better than
copper. These include some soils as well as railway
tunnels and similar locations."
http://www.cable.alcan.com/NR/rdonly...ArmouredEN.pdf
In my 38 years experience, not all but typically most electrical inspectors and engineers state that if the manufacturer says it should be done than it is required for a "workmanlike manner", and that makes it mandated by the NEC.
Due to the age of the pictured disconnects, I am willing to bet that the lugs are not rated for aluminum terminations. And dissimilar metals do require utilization of antioxidant for proper termination, again this is covered under workmanlike manner.
I sincerely hope this helps to provide you with a better understanding of the process of proper terminations for aluminum conductors per NEC.
NOTE: Workmanlike manner is somewhat similar to OSHA's 5(a)(1) General duty clause if it is not specified elsewhere any inspector can call you under this section of the National Electrical Code.
Cordially,
Master Electrician
Fort Worth, Texas
10-02-2010, 04:42 AM #14
Re: Is this okay?
Not to start a debate here , but the neat and workman-like section of the NEC is probably one of the least enforceable. While I am sure most would be able to discern neat work, there is no formal definition in Article 100. What is neat enough for one may not be for someone else. This leaves too much room for interpretation. Suppose you had one inspection with a more relaxed inspector and a followup with a strict inspector that wants corrections when the work has already been approved.
10-02-2010, 12:36 PM #15
Re: Is this okay?
10-03-2010, 07:51 AM #16
Re: Is this okay?
10-03-2010, 10:33 AM #17
Re: Is this okay?
10-04-2010, 08:57 AM #18
Re: Is this okay?
Couple of notes:
Dead fronts are required on residential enclosures, I believe this is a 120/240v commercial?
There usually is a means to bypass the door interlock, thus making it possible to open the door w/o shutting down power.
Unfortunately, the accepted 'workmanlike manner' is per us AHJ's discretion.
10-04-2010, 05:04 PM #19