    Lance Rogers's Avatar
    Lance Rogers Guest
    Default Can AFCI breaker have two wires?
    Can the AFCI breaker have two hot wires installed into one lug? Thanks
    Mar 2009
    Colorado Front Range
    Default Re: Can AFCI breaker have two wires?
    The lug on the breaker is listed for a single conductor. The correct way to wire this would be to install a pigtail on the breaker and wire nut the 2 conductors to it.
    This "fix" appears to have been made to Get AFCI protection on a multiwire branch circuit. GE makes a new style AFCI that can be used on this type circuit - two are used and only one requires the neutral connection, but a handle tie is required between the two.
    Apr 2008
    Western Massachusetts
    You should also note whether that Siemens AFCI breaker is allowed to be used in that enclosure.
    Oct 2010
    Southwest US
    If that's a multiwire circuits, the double tap is the least of the problems. With the circuits on the same phase the neutral will be overloaded. The fix for sure wound not be to pigtail the circuits together!
    Mar 2009
    Quote Originally Posted by Benjamin Thompson View Post
    That would be true if the two hot wires were on separate breakers. Since they are on the same breaker the neutral won't see an overload. If the AFCI was a 20 AMP variety there might be an issue depending on the circuit conductors size.
    Oct 2010
    Southwest US
    Good point, I "forgot" about the circuit breaker that would trip in an overload situation.
    I guess if you consider what an AFCI breaker is supposed to do, there wouldn't be a problem connecting 2 wires as the issue with 2 wires is arcing. If you are going to double tap a breaker, the AFCI would be the one to double tap.
    The default rule is ONE per terminal, connector, lug, etc. when it comes to conductors; UNLESS INDICATED for more than one. INDICATED means marked or labeled.