    Erwin, TN
    Default Double Tap At Main Lug
    Looked in a ITE panel today and found a double tap @ the main lug, but other end went to a ITE Safety Switch box. Would this be acceptable
    Aug 2008
    Default Re: Double Tap At Main Lug
    No, that lug is good for only one conductor.
    Don't forget all those neutrals and grounds in the same terminals with each - that is not allowed either.
    Roger Frazee's Avatar
    Roger Frazee Guest
    To add
    Appears there is no identified neutral ( not a big deal but just pointing it out)
    You probably mentioned it in your report but they could use a few lessons on properly fastening those nm cables in the photo of the safety switch.
    LEO304E CARR's Avatar
    LEO304E CARR Guest
    To add
    All conductors shuld have a seperate connection
    Quote Originally Posted by LEO304E CARR View Post
    Often it's ok to have more than one equipment grounding conductor at the same terminal.