Condo today had a 400 amp disconnect at the exterior closet. Huge copper service wire in Challenger distribution panel in utility room (diameter of wire seemed to be as large as a nickel). Any idea what size copper wires these are.
Any thoughts why a condo complex of 4 units has this much amperage to each unit.
Also the door seemed to weigh 10 pounds and had to be removed to access the recessed dead front cover.
01-31-2011, 07:37 PM #2
01-31-2011, 07:54 PM #3
Re: What size are these service wires?
There were 4 400 amp disconnects. I do not think the wire was new, was much larger than 4/0 and markings were not legible to me.
01-31-2011, 08:05 PM #4
If it is a 400 amp breaker the copper wire should be 400 AWG....
01-31-2011, 08:10 PM #5
Huh?
If the main disconnect size is indeed 400 amps, then the copper conductors would need to be:
- older equipment with 60 degree C rated terminals: 750 kcmil
- newer equipment with 75 degree C rated terminals: 600 kcmil
400 kcmil (which I think you might have been referring to) is only rated for: (respectively based on above equipment)
- 280 amps
- 335 amps
Sidney,
The best way to tell the size is to read the printing on the side of the conductors, shown in white in your photo.
01-31-2011, 08:13 PM #6
Jerrry, Table 310.15(B)(6) would apply here since these are individual dwelling units of a multi-family building, so 400mcm CU is correct.
No way I'd say it actually was 400 unless I saw it on there.
01-31-2011, 08:15 PM #7
01-31-2011, 08:17 PM #8
You are correct, I didn't read far enough when I went back and reviewed:
"(6) 120/240-Volt, 3-Wire, Single-Phase Dwelling Services and Feeders. For individual dwelling units of one-family, two-family, and multifamily dwellings,"
... skipping the: "and multi-family dwellings" part.
01-31-2011, 08:21 PM #9
Unsure if there was a breaker. Only saw the disconnect from the first picture, there were 4 of these and they were not labeled per unit, could not be opened without turning off all power, thus were not opened nor inspected and will write up report that way. I was thinking that these may be inappropriate cable for service wire.
01-31-2011, 08:25 PM #10
01-31-2011, 08:30 PM #11
after magnification, what I can make out on the wiring may be AMD OIL RESISTANT followed by what looks like II, then OB AWM (UL) 600V
Condo constructed in '86
02-03-2011, 10:35 AM #12
In most panels with door handle disconnects ....there is a way to defeat the interloc....so that you can open the door (without turning off power) for inspection, trouble shooting, etc.