Results 1 to 3 of 3
Thread: ground
04-12-2011, 07:11 PM #1
ground
hey you sparkys when using a voltmeter and you test one probe to say a
contactor or relay switch and the other probe to ground screw what is this doing say like when across a switch should read closed zero difference
but one to ground reads 24volts what is this telling you is going on?
04-12-2011, 07:55 PM #2
Re: ground
Tells me you are reading the contactor pull-in coil which will have (typically) 24 volts on one terminal and ground on the other.
I suspect you are measuring the coil terminal and not the actual contractor terminal.
04-12-2011, 10:12 PM #3
Re: ground
Tony
This is a home inspectors site and generally we do not go into detail answering how an electrical device works our how to troubleshoot electrical circuits. However I do agree with Jerry.
Take your question here Electrical - DIY Chatroom - DIY Home Improvement Forum and the electricians that hang out in that forum will answer your questions in detail. Tell them Stubbie referred you if I'm not on line at the time you post..