    Jul 2009
    Spokane, WA
    Default Light fixture above the bathtub
    Is there a specific code that prohibits installing a hanging light fixture above a bathtub? Thanks in advance for your help.
    Inspection Referral SOC
    Aug 2008
    Default Re: Light fixture above the bathtub
    Article 410.4(D) is the part you need.
    Bathtub and Shower Areas. No parts of cord-connected luminaires, hanging fixtures, lighting track, pendants or ceiling suspended paddle fans shall be located within a zone measured 3' horizontally and 8' vertically from the top of the bathtub rim or shower stall threshold. This zone is all encompassing and includes the zone directly over the tub or shower stall.
    The fixture would also need to be at least damp rated. It does not matter in this case since the fixture is within the prohibited zone for that type of fixture.
    Mar 2008
    Charlotte NC
    Looks like a 12' ceiling. Might be 8' above the tub?
    Jul 2009
    Spokane, WA
    That's what I needed. Thank you Jim!
    Aug 2008
    Using the door height as 6'-8 I don't think this fixture meets the 8' distance above the tub.
    Mar 2008
    Charlotte NC
    Could be the angle of the dangle