I was wanting to kmnow if anyone has ever seen regular 12-3 wire with a green wire coming from it that is small. Like speaker wire almost. Was not able to follow all the way being as the box was a real rats nest. Am positive it came from the 12 gauge wire. Thanks
Similar Threads:E.D.S
Home Inspections
Lic.#450.010534
11-26-2011, 02:31 PM #2
Re: small green wire
This may be an EGC from early generation NM cable.
11-26-2011, 10:29 PM #3
11-27-2011, 03:35 AM #4
Back in the days of reduced size grounding conductors in NM cable some manufacturers used a wire with green insulation. I've seen both round insulation (looks like the other wires only smaller) and like this )( where the black and white nestled into the green insulation. The wire wasn't always completely covered by the second type. I saw this stuff installed new in the late mid 60s.
11-27-2011, 07:40 PM #5
Sometime in the early 1970's the 16 AWG grounding conductor was replaced w/ a full size conductor. (Same size as the ungrounded & grounded conductors) & W/ some cable manufacturers they did have a green insulated grounded conductor. Maybe some time I can open up a circa 1968 Zinsco bolt-on panelboard that was wired w/ NM cable & green insulated 16 AWG grounding conductors & get a picture. BTW, off topic the Zinsco bolt-on breakers do not seem to have the trouble that their plug-in counterparts have, just super expensive because replacements are only avail. used, a 2-pole 20A was $140.
11-28-2011, 09:20 AM #6
I am currently remodeling a home built in 1956 and have run into a lot of this wire. Both green coated and bare copper. The conductors are 12 gauge but the grounds are 14 for the most part. There were a couple that looked to be 16 gauge. The original receptacles were all 2-wire, 12 guage; but for all the electrical heat (wall & ceiling) and a few 240 volt receptacles (local heating I assume) the wire was 12/2 with ground. All heating was set to pull 15 amps 120 or 240 volt. There were a lot of 15 amp fuses.
11-28-2011, 11:36 AM #7
11-30-2011, 02:34 AM #8
Yes some were 'coated' as mentioned, but not insulated, as it were.
It was more of a very thin coating and appeared to have been applied at time of manufacturing rather than time of assembling.
12-02-2011, 05:28 PM #9
Don't see any of this wire for a couple of years, then someone posts a comment about it and I get 3 in a week...
12-02-2011, 05:36 PM #10
Sorry, I meant to attach pic
12-03-2011, 04:02 PM #11
Remember "covered or bare" in the NEC code regarding EGC? Well this is a covered GEC.
I suppose a bare EGC in a sheath such as NM could be considered covered?