Results 1 to 11 of 11
    Default 20 Amp AFCI overfusing
    Today I inspected a "total rehab" with a new 200 Amp panel with a city inspection sticker on it.
    All of the AFCI circuit breakers were 20 Amp, with #14 conductors.
    Did this guy just not have any 15 Amp AFCIs in the truck? Why would someone think this was ok?
    Robert Meier's Avatar
    Robert Meier Guest
    Default Re: 20 Amp AFCI overfusing
    A clear violation. NEC 240.4(D).
    Drugs?
    Apr 2007
    WESTMINSTER CO
    call the city inspector and ask wtf
    cvf
    Mount Pleasant, SC
    disregard
    Last edited by Mike Gault; 01-24-2012 at 07:51 AM. Reason: made no sense - referenced 240.4 (G)
    We know why you fly: because the bus is too expensive and the railroad has a dress code...
    www.atozinspector.com
    Apr 2008
    Western Massachusetts
    Probably. They're the same price and, well, it's a hassle driving back down to the supply shop.
    Robert Meier Guest
    Does he own a codebook?
    cuba_pete's Avatar
    cuba_pete Guest
    Did the city inspector own a code book?
    Mar 2011
    Virginia Beach, VA
    Not to belabor the "knowns", 20 OPD with a 14 AWG conductor, but I am curious as to how you made the determination that these were 14 AWG conductors.
    Did you pull the panelboard cover and view the connections on the panelboard? Or do just about all of the conductors going into this panelboard have 14 AWG on the cable sheaths?
    Aug 2008
    Based on this being a recent rehab it would not be had to see the gauge of the wiring used with type NM cables due to the color coding of the sheath. Also looking at a conductor you should be able to recognize the size.
    Quote Originally Posted by Donald Farrell View Post
    Yes, I pulled the cover and looked at the individual conductors and traced them to the cable sheathing, as Jim said.