    Would screwing in a CFU bulb in an old pull chain closet fixture make it a fluorescent luminaire?
    and has 410.8(B) and (D) changed since 2005?
    (D) Location. Luminaires (fixtures) in clothes closets shall
    be permitted to be installed as follows:
    (1) Surface-mounted incandescent luminaires (fixtures) installed
    on the wall above the door or on the ceiling,
    provided there is a minimum clearance of 300 mm
    (12 in.) between the luminaire (fixture) and the nearest
    point of a storage space
    Robert Meier's Avatar
    Robert Meier Guest
    Default Re: CFU's in closets
    IMO no. The requirement is for listed florescent luminaires not incandescent luminaires with CFL lamps.
    410.16 Luminaires in Clothes Closets.
    (A) Luminaire Types Permitted. Listed luminaires of the following types shall be permitted to be installed in a closet:
    (1) A surface-mounted or recessed incandescent luminaire with a completely enclosed lamp
    (2) A surface-mounted or recessed fluorescent luminaire
    (3) Surface-mounted fluorescent or LED luminaires identified as suitable for installation within the storage area
    (B) Luminaire Types Not Permitted. Incandescent luminaires with open or partially enclosed lamps and pendant luminaires or lampholders shall not be permitted.
    Oct 2011
    Minneapolis, MN
    Am I understanding correctly that plain sockets with bare bulbs are not permitted in clothes closets?
    - James Burgh, 1754.
    Chicago
    Quote Originally Posted by Kristi Silber View Post
    That's correct.
    (C) Luminaire (Fixture) Types Not Permitted. Incandescent
    luminaires (fixtures) with open or partially enclosed
    lamps and pendant luminaires (fixtures) or lampholders
    Nope.
    The "fixture" is still an incandescent fixture, the "lamp" has been changed to a compact fluorescent lamp, but ... at any time the lamp can be changed back to an incandescent lamp.
    The fixture itself (to use correct current terminology it is now called a "luminaire" ... sort of ... when you read the definition of "luminaire" you will see what I mean ).
    Mar 2009
    Colorado Front Range
    The language in the 2011 NEC (highlights are mine)
    (A) Luminaire Types Permitted. Only luminaires of the following types shall be permitted in a closet:
    (1) Surface-mounted or recessed incandescent or LED luminaires with completely enclosed light sources
    (2) Surface-mounted or recessed fluorescent luminaires
    (3) Surface-mounted fluorescent or LED luminaires identified as suitable for installation within the closet storage space
    (C) Location. The minimum clearance between luminaires installed in clothes closets and the nearest point of a closet storage space shall be as follows:
    (1) 300 mm (12 in.) for surface-mounted incandescent or LED luminaires with a completely enclosed light source installed on the wall above the door or on the ceiling.
    (2) 150 mm (6 in.) for surface-mounted fluorescent luminaires installed on the wall above the door or on the ceiling.
    (3) 150 mm (6 in.) for recessed incandescent or LED luminaires with a completely enclosed light source installed in the wall or the ceiling.
    (4) 150 mm (6 in.) for recessed fluorescent luminaires installed in the wall or the ceiling.
    (5) Surface-mounted fluorescent or LED luminaires shall be permitted to be installed within the closet storage space where identified for this use.
    Jul 2007
    Chicago
    Pretty sure the intent is the bulbs can break as you pull items off shelving not to mention metal pull chains are a bad idea and those sockets often get exposed when they crack.
    Lost track of how often the wiring is reversed making contact a safety hazard.
    The last part is why they recommend at least a globe which of course takes up more space and can be cracked itself.
    This is why I recommend a florescent strip above the door frame.
    Much depends on shelf location and size of course.