Results 1 to 12 of 12
Thread: Metal pipe bonding
05-13-2012, 08:44 PM #1
Metal pipe bonding
Just checking, when PVC pipes are present do gas and any copper through separation wall still require bonding? I'm feeling like its a yes but wasn't sure.
Similar Threads:Mazza Inspections and stuff...
https://mazzainspections.com
https://waterintrusionspecialist.com
05-13-2012, 08:57 PM #2
Re: Metal pipe bonding
05-14-2012, 06:18 PM #3
Not as easy as that, at least not here in the states ...
- 250.104 Bonding of Piping Systems and Exposed Structural Steel.
- - (A) Metal Water Piping. The metal water piping system shall be bonded as required in (A)(1), (A)(2), or (A)(3) of this section. The bonding jumper(s) shall be installed in accordance with 250.64(A), (B), and (E). The points of attachment of the bonding jumper(s) shall be accessible.
- - - (not posting 1, 2, 3)
- - (B) Other Metal Piping. Where installed in or attached to a building or structure, a metal piping system(s), including gas piping, that is likely to become energized shall be bonded to the service equipment enclosure, the grounded conductor at the service, the grounding electrode conductor where of sufficient size, or the one or more grounding electrodes used. The bonding jumper(s) shall be sized in accordance with 250.122, using the rating of the circuit that is likely to energize the piping system(s). The equipment grounding conductor for the circuit that is likely to energize the piping shall be permitted to serve as the bonding means. The points of attachment of the bonding jumper(s) shall be accessible.
Okay, define "system" ...
In the places that I've been, the riser from the tub valve to the shower head, and the drop to the tub spout are *not* considered a "system".
On the other hand, many builders used to run PB, and now PEX, underground as it can be installed as one continuous piece (no joints to leak), and, where that stubs up through the slab, they would switch to copper. All that copper was a "system" which needed to be bonded, each and every section of it which was discontinuous due to being connected to the plastic underground non-metallic piping.
Is one 10 foot stick of copper a "system"? Probably not.
Is a 50 foot long coil of soft copper run through the house a "system"? Probably.
That is where the code is gray (there really are not many areas which are gray like that) and where the AHJ decides by interpretation.
05-14-2012, 06:24 PM #4
There are some that would not consider it a system unless it was the same material from start to finish. A partially metallic system would not meet their definition.
05-14-2012, 06:57 PM #5
05-14-2012, 07:05 PM #6
In that example I would consider that a system even with the change in materials once the water enters the house.
05-14-2012, 10:08 PM #7
So the reason I'm asking is out here there are a lot of homes re-piped in plastic but have copper in the garage up to the separation wall, then plastic. So its the garage pipes I'm mostly wondering about.
Now that you're speaking about systems, I suppose the gas piping (a system) regardless of the interior supply piping still must be bonded...correct?
05-15-2012, 02:15 AM #8
05-15-2012, 07:31 AM #9
05-15-2012, 07:56 AM #10
IMO it's not required but may offer further protection as outlined in the FPN:
250.104(B) Other Metal Piping. Where installed in or attached to
where of sufficient size, or the one or more grounding elec-
trodes used. The bonding jumper(s) shall be sized in accor-
accessible.
FPN: Bonding all piping and metal air ducts within the
premises will provide additional safety.
05-15-2012, 05:16 PM #11
05-15-2012, 08:43 PM #12
Schooled...thanks.