Results 1 to 22 of 22
Thread: Full New Home Panel
11-20-2012, 08:35 AM #1
Full New Home Panel
I inspected a Brand New 2300Sf home and the service panel is full, I have not run into this in a brand new home! At the risk of asking the "dumb" question is this allowed?
Similar Threads:Jeff Zehnder - Home Inspector, Raleigh, NC
http://www.jjeffzehnder.com/
11-20-2012, 09:25 AM #2
Re: Full New Home Panel
If the sparky left a gap for one breaker, and then a month later, the owners wanted to add a circuit, would that be allowed?
11-20-2012, 09:34 AM #3
Jeff, gotta love when a valid question gets answered with a question. Are we still in Elementary school ?
Paul Kondzich
Ft. Myers, FL.
11-20-2012, 10:07 AM #4
There is no NEC rule regarding the need for future expansion.
Suppose there was a rule that required 5% free space. Would the panel need to be expanded if those spaces were filled in the future?
11-20-2012, 10:13 AM #5
11-20-2012, 10:27 AM #6
The panel looks to be a 30-40 type that allows tandem breakers in the bottom 5 slots. More circuits can be added by swapping single breakers or two pole breakers for tandems or quads in these spaces.
11-20-2012, 10:40 AM #7
11-20-2012, 11:02 AM #8
The panel being full is no problem. When they are full the circuit lableing is sometimes more important than normal. Revealed when you remove the cover, sparkys are not above using a spare circuit breaker to fill KO space that they do not have a blank for. When you have say 30 spaces of C/B blanks to remove it is not always so easy to remove 28 and leave a couple. Using a C/B as a blank filler is fine, if it is labeled as a spare. Smaller branch circuit breakers are relatively inexpensive; especially when bought in volume.
11-20-2012, 12:01 PM #9
11-20-2012, 12:32 PM #10
I was trying to see why someone thought this was an issue. My point was that anything added would be in the future, it would not be added in the past.
11-20-2012, 12:37 PM #11
11-20-2012, 12:56 PM #12
The original poster thought it might be a 'dumb" question. Apparently Jim, you thinks its a dumb question as well. There are no dumb questions.
This post makes me realize why I very rarely check in here anymore. I used to be on every day.
Now its a home buyer asking questions and if they should have an inspection, and things like this, that the "regulars" cant figure out why on earth someone would ask a question like that.
Later it will be people arguing over a word in a code interpretation...
I have to go cut my grass...
Paul Kondzich
Ft. Myers, FL.
11-20-2012, 01:26 PM #13
The NEC is silent on the panelboard being full. I have always used an industry (my Sr. told me so) practice of leaving 2 spaces empty when filling a panelboard, unless I have been given instructions to wire the entire panelboard.
If this is a spec home, I'm surprised not to see two blanks.
What I do see is an unbalanced panelboard, meaning the load (amperage) on on side of the bus is not as close to the other side of the bus, and that is a code requirement. I'll dig up the cite when I get home.
I will concede in advance that it may just be that the picture is just not clear enough.
11-20-2012, 02:28 PM #14
I admit that my question was full of ill intent...
I could not find any "official" reason to state the panel should have room for expansion on this brand new never been occupied 2300SF home but wanted to see what the thoughts of the many would bring.
Thanks to all who took the time to respond.
By the way the new owner will likely add a 3 season room on the rear of the home and it will require some adjustments...
11-20-2012, 02:40 PM #15
I would have wondered the same thing Jeff. Here everything is electric and a small single family is a 200 Amp panel, with plenty of space left. Anything over 2500 sq ft usually has 2x200 amp panels, again with plenty of space left. It was a valid question and unfortunately people here choose to insult, or would rather not answer a question but ask why you would ask a question in the first place.
See you in 3 months, and the grass did get cut.
Paul Kondzich
Ft. Myers, FL.
11-20-2012, 03:36 PM #16
My response was not intended to be a smartazz insult, but so it was interpreted by another, oh well.
I was putting forth a reason why it would not be seen as an issue, and why there is no stipulation for blanks to be left in the panel. I am not a NEC expert, so I left the elaboration for someone else.
Room can be created in this main panel if needed. The buyers can then have a remote panel installed at the back of the house, and this will actually save the cost of running several circuits from the main.
There may be existing circuits back there that can be extended, but that would be up to the electrician to determine.
I have a standard remark on my electrical page, expansion room or no expansion room.
11-20-2012, 03:37 PM #17
11-20-2012, 05:23 PM #18
11-20-2012, 08:07 PM #19
11-22-2012, 06:02 AM #20
I suspect he counted the number of double pole breakers on each side and got 5 on one side and 3 on the other, thinking it should be 4 and 4.
I can think of a way to unbalance a single-phase panel but as Speedy Petey suggested I'd have to go out of my way to do so, and even then so what?
11-22-2012, 07:42 AM #21
The load on a 2 pole breaker is already balanced on both legs. The 2 poles could all be down the left side of the panel and still be balanced.
11-22-2012, 07:44 AM #22
Don't worry about that. You can depend on someone, somewhere, jumping on you for a "smart" question too. But filter the insults, and thin skinned commentary, and a quality answer from someone is usually there. If you are a regular here, you learn pretty quickly who to ignore or dismiss. Kondzich has a good point. If there was less "going personal", there would likely be more participation.