    Erwin, TN
    Default Sub-Panel power off main lug on service panel
    Would it be acceptable to jump off the main lug to power a sub-panel that didn't have a main breaker. Main service panel was a GE 200 amp., the sub-panel didnt have a main breaker. TKS
    Connecticut
    Default Re: Sub-Panel power off main lug on service panel
    no, double tap not allowed.
    main panel more than likely overloaded
    repairs required
    Darrel Hood's Avatar
    Darrel Hood Guest
    Wayne, if the conductor was pig tailed, using proper techniques, to eliminate the double tap, would it be OK?
    Aug 2008
    Wayne, what are you basing your possibly overloaded comment on? Looks?
    'Yes', 'no', and 'not like that', along with 'the remote panel bus would need to be rated the same or higher than the rating of the main disconnect'.