Sub-Panel power off main lug on service panel
Would it be acceptable to jump off the main lug to power a sub-panel that didn't have a main breaker. Main service panel was a GE 200 amp., the sub-panel didnt have a main breaker. TKS
Similar Threads:Last edited by Sam Morris; 02-15-2013 at 07:16 PM. Reason: Pic main panel
02-15-2013, 07:11 PM #2
Re: Sub-Panel power off main lug on service panel
no, double tap not allowed.
main panel more than likely overloaded
repairs required
02-16-2013, 05:04 AM #3
Wayne, if the conductor was pig tailed, using proper techniques, to eliminate the double tap, would it be OK?
02-16-2013, 05:57 AM #4
Wayne, what are you basing your possibly overloaded comment on? Looks?
02-16-2013, 08:39 PM #5
'Yes', 'no', and 'not like that', along with 'the remote panel bus would need to be rated the same or higher than the rating of the main disconnect'.