Results 1 to 10 of 10
Thread: Electrical entrence on roof
02-15-2013, 09:22 PM #1
Hi,
I came across an electrical entrance that was installed on the roof, going under a roof balcony. it is a contractor who renovated the building and I am not familiar with those kind of installation. I wanted to know is it safe?
Thank you
02-15-2013, 09:28 PM #2
Re: Electrical entrence on roof
Was there a service disconnect on the exterior anywhere? Where on the interior was the panel board located and how far does the SEC travel through the interior of the building before reaching the panel board?
02-15-2013, 09:37 PM #3
02-15-2013, 09:46 PM #4
Off the top of my head I'm not sure if the exterior routing across the roof is ok or not. However, the SEC should not travel the distance you listed without having a disconnect before it enters the building. And when a disconnect is on the exterior, the panel board then becomes a sub panel and the equipment grounds and neutrals should be separated. They should only be bonded at the exterior main disconnect.
02-15-2013, 09:52 PM #5
02-16-2013, 05:50 AM #6
Where was the actual connection at the meter? Did it come up the wall and over the roof?
02-16-2013, 07:28 AM #7
02-16-2013, 07:34 AM #8
Those look more like a feeder or branch circuit instead of a service.
02-16-2013, 07:44 AM #9
02-16-2013, 08:42 PM #10
And it entered the hose as soon as it crossed under that deck. From that point on, the disconnect is required to be located 'close to the point of entrance' of the service entrance conductors, i.e., 'close to the point where it goes under the deck'.
Also, the conductors in those conduits need to be derated for being in conduit and on a roof.