Results 1 to 12 of 12
Thread: "Dirty Panel"
10-02-2007, 01:13 PM #1
"Dirty Panel"
From a warranty inspection - guess they electrician has no pride.
Also, all 15A and 20A breakers are all wired with 12 AWG wire. How should i word this in the report?
10-02-2007, 01:50 PM #2
Re: "Dirty Panel"
All foreign debris should be removed from the panel.
No problem with the 12 GA wire to a 15 amp breaker. It might be harder to work with and may not fit back-stab outlets, but it is perfectly fine to use 12 GA wire on a 15 amp circuit, in fact it may be needed under some circumstances.
10-02-2007, 01:53 PM #3
Re: "Dirty Panel"
Rick,
Looks like someone came in after the electrician also when the panel door was open.
If 12 AWG service wire was cooper no problem as it;s rated for 20 amp.
Pictures in summary report needs cleaned would work for me.
I'm sure others will comment on how they report.
10-02-2007, 02:14 PM #4
Re: "Dirty Panel"
Thanks for the replies. I'm not worried about the 12AWG and the 20A breakers it's the 15A breakers. I understand that they are the "weakest link" in the circuit, but I don't understand why they didn't use 14AWG on the 15A circuits. Maybe big sale on the 12AWG!? Also, is this common in new construction? If so, any ideas why?
10-02-2007, 02:48 PM #5
10-02-2007, 03:12 PM #6
Re: "Dirty Panel"
One local jurisdiction around here does not allow any #14 wire for lights and outlets on new construction. It all has to be #12.
10-02-2007, 03:29 PM #7
Re: "Dirty Panel"
The benefit of that, besides the low voltage drop on the conductor itself, is that *BACKSTABBING* is eliminated as #12 cannot be backstabbed into devices, those backstabbing holes are sized for #14 only.
The highest voltage drop cause I've run across on most moderately sized homes is from backstabbing - remove the conductors from the backstabbed hole connections and putting them under the screws *DRAMATICALLY* reduces voltage drop (in my experience, anyway).
On larger homes, the sheer length of the conductor, doubled (hot and neutral) easily makes up 5%-10% voltage drop on #14 wire. A 62-1/2 foot long circuit (125 feet of conductor) give 5% voltage drop for #14 at full 15 amp load, that's a home run. Add in device connections and the voltage drop just goes up and up and up and ... Remember, though, that's 62-1/2 feet of circuit length, not distance, you have to count going up, down, around, sideways, and back down to a device, here is an example: 3' up from the breaker, 22-1/2' sideways (once), 7' back down to a device, with the conductors run taught and straight except that one turn, no other bends or turns, you now only have a distance from the panel to 30 feet from the panel to the device; say the panel is near the front of the garage, that's 20' to the back of the garage, you now only have 10 feet left - that is not going to get you very far at all.
10-02-2007, 04:02 PM #8
Re: "Dirty Panel"
I love the cigarette butt in the panel.... that's always the mark of a good electrician.
Jerry, I'm imagining things? I could swear some heavy duty 20amp gfi receptacles I once bought had backstab holes for 12 gauge...
10-02-2007, 06:21 PM #9
Re: "Dirty Panel"
Matt,
"I once bought"
That's key to what I stated.
The backstab holes 'used to' accept #14 or #12, but not for, maybe, the last 8-10 years or so (don't recall just when that change was made).
That's because so many problems occurred with that pressure contact connection when using them on 20 amp circuits.
10-02-2007, 10:05 PM #10
Re: "Dirty Panel"
Thank you for the replies. It makes sense to me now. I really appreciate the help!
Rick
10-03-2007, 06:38 AM #11
Re: "Dirty Panel"
It is the main panel, Fritz.
10-03-2007, 07:24 PM #12
Re: "Dirty Panel"
"Main Panel"
That means nada for the question as to where the neutrals and grounds are bonded together.
Neutrals and bonds *ARE ONLY* bonded together *at the SERVICE EQUIPMENT*, without regard as to whether or not there is a "panel" there as part of it.