Results 1 to 12 of 12
Thread: GFCI wiring
    Dec 2007
    Holladay, UT
    Default GFCI wiring
    Today's inspection, 1975 house. This is a GFCI breaker for exterior outlets. Could someone explain the short black wire that appears to be some sort of jumper?
    http://acloserlookslc.com/
    Default Re: GFCI wiring
    Sorry Tom,
    Other than "it doesn't look right to me", it's not something I have seen before. Looks like the neutral wire is double tapped.
    Dec 2007
    Holladay, UT
    That's exactly what I thought when I opened the panel, "that just doesn't look right".
    I've seen that jumper before, but in white. And I agree, someone has added another neutral. That's a good reason to have an electrician replace the old breaker and straighten out the wiring.
    Apr 2009
    NY State
    Two wires does not automatically trip the dreaded "double tap" siren.
    Many older GFI breakers had tails for both the line and load neutrals. That is the case here.
    Dec 2007
    Holladay, UT
    By the way the GFCI did trip when tested at breaker and outlets.
    Jun 2010
    Morris County, New Jersey
    ITE was acquired by Gould in the mid-1970s and Gould / ITE was bought by Siemens about 10 years after that - this breaker is almost 40 years old. See this link for a comment on a similar GFCI jumpered breaker: GFCI circuit breaker - InterNACHI Inspection Forum
    Mbrooke's Avatar
    Mbrooke Guest
    The breaker doesn't stand out to much for me, the set up looks like a factory makeup. Double tap most likely (but I cant tell for sure) is the normal required branch neutral. The white-black stripe is the factory neutral jumper over to the neutral buss bar.
    I would be more concerned about the other breakers, they have an FPE flavor, ie they resemble challenger breakers.
    What brand are those red handle breakers and what brand is the panel itself?
    May 2009
    Washington State
    Default Re: GFCI wiring - WTF are these? No Test Buttons?
    Ran into these yesterday in a 125 Amp Cutler Hammer Panel - never seen them before. Looking how clean and new the stickers look as opposed to the banged-up toggle, I think someone had a "Baby Label Maker" !
    Dec 2007
    Holladay, UT
    Mbrooke, The inspection was 3 inspections ago but looking back through my pictures I believe panel,and breakers are ITE.
    Apr 2009
    NY State
    Quote Originally Posted by Jim Hintz View Post
    Not sure if you are being serious or not, but those are NOT GFI breakers, and those are the stickers that come with GFI receptacles.
    Dec 2007
    Chico,Ca
    The panel is not ITE, & the twin breakers look like old style Murray, made before Murray became Crouse-Hinds, my guess is the panel is Murray or Bryant.