Results 1 to 11 of 11
04-07-2014, 01:56 PM #1
04-07-2014, 03:17 PM #2
Re: Main Panel or Subpanel in unit where main disconnect is in basement
04-07-2014, 04:13 PM #3
A sub in the unit itself would be a normal installation while the service is in an electrical room with the meters.
04-07-2014, 06:55 PM #4
If, the main disconnect is else where, any panel after that automatically becomes a subpanel. The panel should be fed via 4 wires hot, hot, neutral and ground that being either metal conduit, a green wire, or a bare wire, or the 4th wire bare in SER cable. The neutral bar is left floating.
Any pics to verify?
04-07-2014, 07:10 PM #5
Melvin,
Regardless if there is a disconnect in the condo unit's panel (no single 'main' disconnect is required in the condo unit's panel), the "service equipment and service disconnect" is elsewhere at the service equipment of the building, thus the neutral and grounds are bonded together at the service equipment, and the neutral is isolated from ground at all points after the service equipment (which is not even that condo unit main in the basement).
It is extremely nice to have a 'panel main' at the unit's panel, just not required.
04-08-2014, 03:46 AM #6
Thanks for your feedback. Just needed confirmation, since it is a large condominium and other units are likely to have similiar wiring.
I tried to attach a picture. Am new to this site.
There are other issues as well as misuse of tandem breakers, double tap.
04-08-2014, 06:03 AM #7
04-08-2014, 07:53 AM #8
04-08-2014, 09:24 AM #9
04-08-2014, 06:01 PM #10
Sub's cannot be bonded to ground. The rod through the hull causes leaks.
04-08-2014, 06:34 PM #11