Thread: Copper supply bonding
07-22-2014, 04:22 PM #1
Kind of a Florida question where most homes are on slabs. I was hoping I could get a discussion going on bonding the copper or galvanized supply piping to the electrical system. On most homes; I usually find it at the water heater but on some I do not and can't find it elsewhere. If I can't locate it; I just make a note and recommend electrician confirm that the system is properly bonded. Maybe some of the experts can give some incite as other areas it may be found that may not be visible. Also; is there a simple procedure to determine if the bond is present or anything else that would pertain to this subject. Thanks
07-22-2014, 06:04 PM #2
Re: Copper supply bonding
Are you asking about bonding or the GEC connection to a metallic water line?
If the GEC it should be within 5' of were it enters the building on newer homes. Older editions allowed the connection to be anywhere. Normally this was close to the panel to cut down on the wire run.
07-22-2014, 07:20 PM #3
07-22-2014, 08:58 PM #4
Not an inspector but I would not think it would be that hard to find. Are you sure the water line is metallic and in contact with the earth for ten foot or more?
07-23-2014, 03:42 AM #5
07-23-2014, 05:56 AM #6
If the pipe system in the structure is metallic it must be bonded. Small pieces of metallic pipe used for connections to fixtures would usually be exempt. I often find repairs to copper pipe systems made with non metallic pipe and these repairs need to have bonding jumpers that bridge the repair and seldom see them installed. The bonding and grounding electrode connections to pipe are required to be accessible (with exceptions not normally found in residential type installations.)
Bonding is to keep metal pipes (and consequently attached fixtures) from becoming energized (and staying that way) because of an electrical fault.
Various gas appliances are allowed to be the bonding connection for gas lines so you seldom find a separate bond for the gas lines, but some means needs to be present to bond them.
07-23-2014, 06:38 AM #7
I don't look in every nook and cranny of the house and plumbing to find the GEC. If it isn't obvious, I simple note that I didn't find it. Most of the time, the outlets show grounds, but of course, that doesn't mean the system has a compliant GEC.
07-23-2014, 01:57 PM #8
A receptacle showing as grounded has absolutely nothing to due with the presence or lack of a GEC.