	07-23-2014, 01:22 PM #1 Grounding to water supply from feeder panel Grounding to water supply from feeder panelIs it permitted to run a ground wire to the water supply pipe from the feeder panel ground terminals instead of from the main panel? In this installation the grounding electrode was run from the main panel, but the ground to the water supply pipe was run from the feeder panel.
	07-23-2014, 01:58 PM #2 Re: Grounding to water supply from feeder panel Re: Grounding to water supply from feeder panelThe grounding needs to come from the service panel.
	07-23-2014, 02:59 PM #3
	07-23-2014, 05:48 PM #4 Re: Grounding to water supply from feeder panel Re: Grounding to water supply from feeder panelI would need to look it up to be sure, but bonding of the interior water piping system may not be required to be directly bonded to the service equipment as bonding to the groundING conductor in a remote panel bonds the metal water piping back to the service equipment to.
 Jim P what say you? I can look it up later.
	07-23-2014, 06:47 PM #5 Re: Grounding to water supply from feeder panel Re: Grounding to water supply from feeder panelI have never done it that way and don't know whether it would fly or not. Jack D would know
	07-23-2014, 07:10 PM #6 Re: Grounding to water supply from feeder panel Re: Grounding to water supply from feeder panelI just got back to my office and looked it up, the answer is yes and no ... sort of.
 From the 2008 NEC (on my computer for easy copy and paste): (bold and underlining are mine)
 - 250.104 Bonding of Piping Systems and Exposed Structural Steel.
 - - (A) Metal Water Piping. The metal water piping system shall be bonded as required in (A)(1), (A)(2), or (A)(3) of this section. The bonding jumper(s) shall be installed in accordance with 250.64(A), (B), and (E). The points of attachment of the bonding jumper(s) shall be accessible.
 - - - (1) General. Metal water piping system(s) installed in or attached to a building or structure shall be bonded to the service equipment enclosure, the grounded conductor at the service, the grounding electrode conductor where of sufficient size, or to the one or more grounding electrodes used. The bonding jumper(s) shall be sized in accordance with Table 250.66 except as permitted in 250.104(A)(2) and (A)(3).
 - - - (2) Buildings of Multiple Occupancy. (basically not applicable to houses)
 - - - (3) Multiple Buildings or Structures Supplied by a Feeder(s) or Branch Circuit(s). (not likely applicable to most houses in most cases)
 If the grounding conductor to a remote panel met the requirements of 250.104(A)(1), then I can see that being permitted as the bonding jumper (for a potential 'yes' answer), otherwise the answer would be 'no, needs to be bonded at the service equipment'.
	07-25-2014, 07:43 AM #7 Re: Grounding to water supply from feeder panel
		Mazza Inspections and stuff... Re: Grounding to water supply from feeder panel
 https://mazzainspections.com
 https://waterintrusionspecialist.com
	07-25-2014, 09:14 AM #8 Re: Grounding to water supply from feeder panel Re: Grounding to water supply from feeder panelMarc,
 I will rephrase the above: bonding to downstream panels may bond the metal water piping back to the service equipment by proxy, but ... "technically" ... it does not bond the metal water piping back to the service equipment unless the bonding conductor meets the requirements for the bonding conductor.
 It may accidentally bond it to the service equipment by proxy ... but I would not like to rely on accidents happening at the precise time the accident needs to happen.
  Reply With Quote Originally Posted by Jim Port
 ...by bonding the panels downstream to the SEP (which connect to the SEP), "technically" bonds the water piping by proxy?
