Results 1 to 14 of 14
Thread: No ground?
09-30-2014, 10:28 AM #1
No ground?
I inspected this sub-panel today and did not see a ground. It appears it was for a hot tub on the rear porch...which is now gone. The breaker was turned off. As you can see it is 50A, 220V. Am I missing something or shouldn't this have a ground wire in there somewhere?
PS. The black wire coming from below does not enter the panel....that is a Coax TV wire that goes behind it.
Dave
09-30-2014, 11:20 AM #2
Re: No ground?
Yes, an equipment ground is required.
09-30-2014, 12:15 PM #3
Re: No ground?
09-30-2014, 06:29 PM #4
Re: No ground?
09-30-2014, 07:49 PM #5
Re: No ground?
No, it is on the back burner simmering, waiting for the right times to be spoon fed to others ... Elvis has not left the building, that was an Elvis impersonator who left.
What about that conduit? Is it possibly providing grounding for the panel box?
10-01-2014, 05:55 AM #6
10-01-2014, 01:57 PM #7
Re: No ground?
As far As I know the ground would be required.
10-02-2014, 06:04 AM #8
10-02-2014, 06:46 AM #9
Re: No ground?
10-02-2014, 06:53 AM #10
Re: No ground?
Hi All, My understanding of a sub panel is this:
1.Both conduit & NM cable system require a floating neutral isolated from the ground in a sub panel. There are mechanical differences between the 2
2. The basic rule is : Don't connect grounds with neural at any point after the main.
3. In a conduit system, no ground conductors are brought into the sub panel enclosure, because the enclosure is part of the ground conductor system .
Because parallel path could cause: Fires, High levels of electro magnetic issue (problematic for PC's and other sensitive equipment. shock hazards etc. Especially with a weak neutral connection.
Further, Bonding grounds & neutral in a sub panel will allow neutral current to be also carried on the grounding conductors, including any bonded metal components with in the ground path.
Hope this helps
10-02-2014, 07:10 AM #11
Re: No ground?
Sub panels are found in submarines.
That panel is a downstream panel ... a remote panel ... or just a panel ...
The only panel with a specific name is the "service equipment" panel.
With that said and out of the way ...
[Quote]
1.Both conduit & NM cable system require a floating neutral isolated from the ground in a sub panel. There are mechanical differences between the 2[/quote ]
The only mechanical difference is a bonding connection connecting the neutral to ground - to me, that is an electrical difference instead of a mechanical difference.
10-02-2014, 08:13 AM #12
Re: No ground?
Article 250.118 says conduit is a suitable ground conductor, provided the over current protection does not exceed 20 amperes, for a 1/2" conduit. In this case, the OCP is 50 amperes, which is excessive for a hot tub, but still is 50 amperes. The conduit is larger than 1/2", and therefore the 20 amp limit for conduit does not apply.
250.118 Types of Equipment Grounding
Conductors. The equipment grounding conductor run with or enclosing the circuit conductors shall be one or more or a combination of the following:
(1) A copper, aluminum, or copper-clad aluminum conductor. This conductor shall be solid or stranded; insulated, covered, or bare; and in the form of a wire or a busbar of any shape.
(2) Rigid metal conduit.
(3) Intermediate metal conduit.
(4) Electrical metallic tubing with an additional equipment grounding conductor.
(5) Listed flexible metal conduit with an additional equipment grounding conductor,
and meeting all the following conditions:
a. The conduit is terminated in fittings listed for grounding.
b. The combined length of flexible metal conduit and liquidtight flexible metal conduit in the same ground return path does not exceed 1.8 m (6 ft) for feeders and 15 m (50 ft) for branch circuits.
c. The additional equipment grounding
conductor is terminated at each termination or junction point.
(6) Listed liquidtight flexible metal conduit meeting all the following conditions:
b. For metric designators 12 through 16 (trade sizes 3/8 through 1/2), the circuit conductors contained in the conduit are protected by overcurrent devices rated at 20 amperes or less.
10-02-2014, 10:10 AM #13
Re: No ground?
10-06-2014, 10:20 AM #14
Re: No ground?
Thanks everyone, it seems someone forgot the ground....just surprised me...thought I may be missing something easy. The conduit is plastic.
- - - Updated - - -