Hi, need to learn about below water line pool lights and GFCI protection.
Questions:
(1) I know that 120v lights should have it but not sure about more modern lights that are low voltage
(2) If low voltage lights require it; when did that go into effect by the NEC
10-09-2014, 12:16 PM #2
Re: Pool lights and GFCI protection
The power supply to the transformer can be GFCI protected but once the power is stepped down (pool side) you do not have the protection of the GFCI. I do not know of a GFCI protection for low voltage, as far as I know GFCI is only for 120v.
10-09-2014, 12:42 PM #3
10-09-2014, 12:58 PM #4
What does the 2008 NEC say?
Most of the places in my area are on the 2012 NEC.
I don't inspect pools, most of the pools in the homes I inspect cost as much or more than my $200k home! I tell my clients to contact a pool specialist, just too many things to keep up with and the liability with pools is so great I just do not want to mess with them. I know that in many areas the home inspector is expected to inspect the pool, I'm glad that is not the case in my area.
10-09-2014, 01:15 PM #5
From the 2008 NEC: (underlining is mine)
- 680.23 Underwater Luminaires.
- - This section covers all luminaires installed below the normal water level of the pool.
- - (A) General.
- - - (3) GFCI Protection, Relamping. A ground-fault circuit interrupter shall be installed in the branch circuit supplying luminaires operating at more than 15 volts such that there is no shock hazard during relamping. The installation of the ground-fault circuit interrupter shall be such that there is no shock hazard with any likely fault-condition combination that involves a person in a conductive path from any ungrounded part of the branch circuit or the luminaire to ground.