    Does anyone see anything wrong with this 100 amp downstream service panel ? Aren't the neutral and grounds suppose to be separated in a aka sub-panel ? Thanks in advance
    Default Re: AKA Sub-Panel
    Yes he should have installed a grounding bus on the back of the panel box for the grounding conductors.
    He should have provided grounding to the panel box with a 4th conductor. It is all wrong.
    Dec 2007
    Chico,Ca
    In addition to being wrong because of not having a equipment grounding conductor, the Siemens breakers in that GE panel do not belong there.
    Oct 2012
    Massacusetts
    the Siemens breakers in that GE panel do not belong there.[/QUOTE]
    We need to call you Hawk eye . what are you using that allowed you to enlarge the photo from the screen , or do have to save it then open it another application ?
    Jan 2013
    MA
    The service feed to the panel box is only two wire wire with a ground, it should be three wire with a ground.
    Mar 2012
    Wisconsin
    Red face Re: AKA Sub-Panel
    We need to call you Hawk eye . what are you using that allowed you to enlarge the photo from the screen , or do have to save it then open it another application ?[/QUOTE]
    Right click on the picture. In the drop down menu select "save picture as". Save the picture in (Pictures) on your computer. Open the (Pictures) on you computer and you can then zoom in on it.
    Quote Originally Posted by Mike Borchardt View Post
    From Brian I got this - Open the pic on your desktop and use 'cntrl' and '+' to zoom.
    Dec 2007
    Chico,Ca
    I just opened the thumbnails, ITE / Siemens breakers are pretty easy to recognize.