Results 1 to 16 of 16
06-26-2015, 03:55 PM #1
Are these other wires and systems allowable around Masthead?
I recommended Buyer remove these plug in wires for snow melt system due to proximity with main service wires, but is there anything against this in the code? Is the outlet box proximity to the service head allowable? (The bedroom window is right there as well)
Also in case you were not aware, there is a new way to bunch all the grounds in a main panel into a ball and pretend to clamp them without a bus bar...
Similar Threads:Last edited by chris vis; 06-26-2015 at 04:44 PM.
06-26-2015, 05:21 PM #2
Re: Are these other wires and systems allowable around Masthead?
While there is really nothing which is right about those receptacles up there - the one item which is not wrong (not prohibited) is being that close to the service conductors.
Also, the grounds in that service equipment panel (I am presuming it is the service equipment panel) are really all fudged up.
It does look like the neutral terminal bar is bonded to ground (at the top of the left neutral terminal bar).
07-01-2015, 05:15 AM #3
I do see an issue with the ground wires , each needs to be secured individually - it appears someone used and all in one clamp to satisfy this - chances are there is a floating ground too (one that is not really connected (electrically to the rest) - for this reason alone - I would suggest having an electrician come in and evaluate the electrical system - it is a big enough error that you want more trained eyes (and equipment looking at it)
The De-icing cables , Look like you have to plug them in to use them - just guessing but I would not want to be up on a ladder doing that and the outlet leeds me to believe this was a do it yourself add on and not properly protected - my guess is you need to turn on the light to activate them
- - - Updated - - -
07-01-2015, 05:49 AM #4
I am fairly certain that you can't run another wire up the service mast and out to that outlet. That's one that I've never seen and while creative....no bueno!
07-01-2015, 06:29 AM #5
2014 NEC
230.28 Service Masts as Supports. Only power service drop or overhead service conductors shall be permitted to be attached to a service mast. Service masts used for the
support of service-drop or overhead service conductors shall be installed in accordance with 230.28(A) and (B).
07-01-2015, 09:34 AM #6
07-01-2015, 06:48 PM #7
07-03-2015, 03:32 AM #8
What a nightmare!!
First, draw a line 3' from the window in all directions. That is the required clearance.
I do believe the masthead should have an 18" clearance in all directions. Even if its less its too close to the soffit. Much too dangerous to service whatever is plugged in to the plugs or even change the light bulb. As for the panel...the enclosure is not bonded, each ground conductor is required to be mechanically secured and torqued??? (is that a word)as specified. I can't see the size of the main, but i'm pretty sure the aluminum service entrance cables are undersized.
07-03-2015, 09:01 AM #9
It is? In all directions? Where did you get that from?
07-03-2015, 11:52 AM #10
Thanks Jerry, I was wondering where some of those rules were coming from too. Hope she explains her ideas.
07-03-2015, 12:17 PM #11
I accept the challenge
although surprised your questioning the window clearance.
like i said the 18" clearance for masthead i'm unsure but i do know all parts must be accessible for servicing, without disassembling the structure, hence the mastheadhead is too close to soffit.
all devices,parts shall be approved for their application. The ground clamp is listed for a single conducted/ground rod connection. ill get you code reference on the window clearance.
and look at pic of enclosure again
so your saying the enclosure is properly bonded because the neutral bar has a strap?
07-03-2015, 12:47 PM #12
I see a bonding bar that runs between the bus bars. it appears to be properly secure but that does not bond the enclosure. the only source of ground (earth ground) that achieves equal potential to the service entrance and protection for equipment and occupants is the #4bare copper that should go to the ground rod. make sense?
ok code reference for clearance from a fire escape!
07-03-2015, 01:18 PM #13
<br><br>
I see a bonding bar that runs between the bus bars. it appears to be properly secure but that does not bond the enclosure. the only source of ground (earth ground) that achieves equal potential to the service entrance and protection for equipment and occupants is the #4bare copper that should come from the ground rod. make sense?<br><br>
ok code reference for clearance from a fire escape!<br>
<br>
<font color="silver">- - - Updated - - -</font><br>
<br>
<br>
i stand corrected nec 230.9 requires clearance for windows on three sides(2 sides and bottom) from service drop, not the top<img src="http://www.inspectionnews.net/home_inspection/images/smilies/redface.png" border="0" alt="" title="Embarrassment" smilieid="2" class="inlineimg">
07-03-2015, 04:32 PM #14
07-03-2015, 05:00 PM #15
We'll still be here.
07-03-2015, 07:09 PM #16
Mary, the conductor to a ground for never has to be larger than a #6.
- - - Updated - - -