Thread: Distribution panel wiring
12-04-2015, 10:48 AM #1
I know this is a broken record, but, Main panel on pole comes into dist panels with 3 wires, neut and grounds not isolated. I assume there should be 4 wires from pole to house dist panels, isolated neut and gr in house dist panels.
12-05-2015, 11:06 AM #2
Re: Distribution panel wiring
The panel at the pole is the distribution panel and needs to be grounded there (those two big white conductors dropping out of the bottom may be your insulated grounds connected to a couple of driven rods "x" feet apart). Three wires to the other panels in the house/barn/garage or where ever the first picture is taken. Those two panels in the picture need to have the ground bar bonded to the panel and the neutral bar floating to be correct. It appears that in the left panel this is not the case. Can't tell if right panel is done correctly from the picture.
12-05-2015, 02:24 PM #3
Russell,
Are there any other wires going to/from the pole? Such as phone wires?
The panel on the pole is the service equipment.
All other panels are downstream of the service equipment, however, the first panel in/on the next structure (the house/garage/whatever) has different grounding and neutral bonding requirements than panels downstream of those first panels on the structure.
12-19-2015, 09:17 PM #4
The panel looks old enough to be from the era when 3-wire feeds were allowed between structures, yes, the pole is a "structure".
12-20-2015, 10:53 AM #5