Results 1 to 9 of 9
Thread: Ufer ground
02-25-2016, 04:35 AM #1
Ufer ground
In concrete construction I may come across 2 aluminium conductors at the water main pipe.
One attached to the water pipe at the sub-out, the service ground, the other exposed several inches but not connected to the main water pipe.
My questions are, would this be a Ufer visual verification point.
If so do you address the conductor in the report.
Thanks in advance.
Similar Threads:Robert Young's Montreal Home Inspection Services Inc.
02-25-2016, 11:42 AM #2
Re: Ufer ground
If they're aluminum, it is a code violation. Ufers should be terminated at the service disconnect.
They look like copper to me.
02-25-2016, 01:27 PM #3
Re: Ufer ground
Brad thank you.
I concur. It certainly looks like copper.
The patina on the copper had me confused.
Aluminium feeds are typical in developments in my neck of the woods.
Time to open dead fronts again when I can.
Best regards.
02-26-2016, 04:38 AM #4
Re: Ufer ground
Robert,
I don't know about Que. but in Ontario Aluminum is not used for grounding only copper as aluminum is prone to corrosion. They do use aluminum for feeders from the street though since copper is pretty pricey.
Judging by the valve that's an older incoming water line and me thinks that you likely have grounding rods used rather than Uffer or they used the incoming water line for ground.
02-26-2016, 06:45 AM #5
Re: Ufer ground
Is there a requirement that the wire be solid???
02-26-2016, 07:46 AM #6
Re: Ufer ground
Its all stranded.
02-26-2016, 10:27 AM #7
Re: Ufer ground
02-26-2016, 02:56 PM #8
Re: Ufer ground
According to the Cdn Elect. Code
1. The conductor must be bare
2. Conductor must be copper
3. Two ground rods minimum, sometimes more may be required.
4. Ten feet apart
Six ga. is minimum or larger to connect the ground rods together and back to service panel.
For water piping -
Ten feet is required of continuously conductive metal water piping system that is located underground at least 24 inches below finished grade.
Concrete Encased Electrode -
1. Single copper conductor
2. Four ga. or larger
3. At least 20 ft. long (min.) but can be longer
Sections above were taken from PS KNIGHT Electrical Code Simplified based on 22nd Edition of Ont. Elec. Safety Code.
02-26-2016, 08:17 PM #9
Re: Ufer ground