Thread: Remote panel in remote building
05-25-2016, 05:39 AM #1
This remote panel is located in a detached building and has a secondary ground connection. (which I believe must be provided??) Should this second ground be connected to the isolated neutral terminal bar as shown in the picture??
05-25-2016, 11:41 AM #2
Re: Remote panel in remote building
If the feeder is 4 wires, the ground needs to be on the isolated ground bar. This bar would also have the connection from the ground rod. No bond screw or strap should be installed.
05-26-2016, 08:45 PM #3
05-27-2016, 02:20 PM #4
The isolation is from the neutral. The ground bus is screwed to the enclosure.
05-27-2016, 06:57 PM #5
No more sub panels?
Making some here happy
05-27-2016, 09:16 PM #6