    Oct 2010
    MONTREAL QUEBEC-CANADA
    Default Point of attachment for service-drop conductors
    Over head service drop.
    1: Mechanical connector is taped. No weather shield.
    3: Drip loop roof clearance.
    Any issues? I have looked through article 230 and can not determine any issues as of yet.
    Much thanks.
    Default Re: Point of attachment for service-drop conductors
    First photo:
    - No flashing where mast penetrates roof.
    Second photo:
    - Neutral (grounded conductor) coming out of mast/weather head to overhead service drop appears smaller than other conductors, looks to be a lot smaller.
    - Minimum height of lowest conductor (including drip loop) above the roof is 18"
    - Maximum roof crossed is 4'.
    - Maximum conductor length crossing roof is 6' (allows for diagonal length increase over the 4 foot roof area being crossed).
    - Roof area being crossed is the overhang only (mast is on exterior wall, going up on the outside of the exterior wall).
    Those should work for starters in those photos.
    Oct 2010
    Mast boot flashing is covered.
    Modified roof was poorly applied. Amateur mistakes throughout.
    Thanks for drip-loop/roof deck height/clearance requirements.
    I will review the neutral.
    Sep 2012
    Columbus, OH
    If that's a service feed ahead of the meter, you would need to check the utility's requirements--the NEC doesn't govern them.
    Quote Originally Posted by Jason V. Advani View Post
    The NEC addresses up to the point of attached (utility's point of connection - the utility's splices) of the overhead service drop to the service entrance conductors protruding from the mast weatherhead.
    Oct 2010
    First photo:
    Reported.
    Second photo:
    If you look at the feed and SEC neutral gauge at wire nut, the are the same.
    Covered.
    <48 inches.
    <72"
    - Roof area being crossed is the overhang only (mast is on exterior wall, going up on the outside of the exterior wall). Yes.
    Thanks Jerry.