12-14-2017, 06:59 PM #1
60 amp breaker in Main panel feeding panel in garage with 100 amp main.
I have just looked at a main panel in a basement with a 60 amp breaker (100 amp service). This breaker feeds another panel in a garage with a 100 amp main breaker and panel... what are the implications? Thanks in advance...jb
12-14-2017, 10:05 PM #2
Re: 60 amp breaker in Main panel feeding panel in garage with 100 amp main.
12-15-2017, 09:31 AM #3
I was waiting for Gunnar to comment on the terminology and that the use of "main panel" indicated a different panel than the "service equipment" panel. (For those who believe that "main panel" means the "service equipment" panel.)
I PRESUME that what is being described is:
a) The service equipment panel is someplace else and is apparently 100 amp rated (because of the "100 amp service" statement, however ... this statement 'could' be indicating that this panel in the basement IS the "service equipment" panel and what is being described is just one of the breakers in that panel which feeds the other panel in the garage).
b) The panel in the basement is a remote panel (remote from the service equipment panel located elsewhere - see a) above ... but might not be ... just not enough information in the description to know for sure).
c) The panel in the basement has a 60 amp breaker which feeds another panel in the garage which has a 'panel main' of 100 amp.
Basically, though, as Gunnar said:
Originally Posted by Gunnar Alquist
12-15-2017, 10:09 AM #4
How about you tell us what you see as the issue?
12-15-2017, 11:31 AM #5
When you see a 30 to 60 amp feed added to the home panel, going outside to a shed, and if it is a good bet it was done by someone other than a certified electrician - Check the wire gauge of the feeder, and check where it leaves and enters the other building.
For 240 volt service to the shop there needs to be 4 wires in that cable.
Check for a bond from the shop panel back to the source panel or main panel.
The panel in the shop has a main disconnect and that is good. The service to the shop is 60 amps, provided the wire gauge is sized to handle 60 amps. If it is undersized cable, the breaker needs to be replaced.
12-15-2017, 07:43 PM #6
12-15-2017, 07:51 PM #7