Thread: Bathroom Water Heater
01-23-2008, 09:25 PM #1
OK, I'm trying to help a friend, so don't lecture about the obvious. His house has a small electric water heater under the vanity in an addition bathroom. The electric water heater has a NM cable and plug (i.e. Romex) plugged into a 15 amp receptacle under the vanity. The NM cable was called out by the home inspection as being unsafe. The wiring is behind the water heater, and there is very little access to the receptacle or the wiring without removing the entire water heater from under the vanity, if it will even fit out of the cabinet doors.
So, the proper cable is to be protected by flex or MC cable.
My questions are: 1: Is the protection of wires applicable in all locations, including underneath a vanity? I only wonder because a garbage disposal with a flex cord plugged into a receptacle is perfectly ok in our world, but a disposal with a NM cable plugged into a cord is not, which I never really understood. Romex is that much weaker than a flex cord and plug? Not that it has to make sense. I don't see how this cord would be subject to any physical damage, but maybe that doesn't matter in this case. Hell, you can barely even see the thing under the vanity.
To replace the wiring with a flex conduit, not to mention some type of disconnect under the vanity would be a lengthy job. It would involve removing the entire water heater, replacing the wiring, re-installing the water heater, etc. On looking at the install, I thought about installing a GFCI breaker on the power supply to the water heater.
Question 2: Would a GFCI not satisfy the intent of protecting the wiring on an electric water heater, even though it may not be specifically addressed in the NEC?
I'm just trying to help out without having to remove and rewire the entire water heater, which I'm thinking would take almost a whole day for what I'm seeing as very little benefit to the homeowner.
Any suggestions would be appreciated.
Similar Threads:Jim Robinson
01-24-2008, 12:36 AM #2
Re: Bathroom Water Heater
Jim,
To my way of thinking, there is a difference between "wrong" and "unsafe". I doubt that I would have written "unsafe" in my report.
That said, I would check with the manufacturer of the water heater or review the installation instructions. It may be that an appliance cord (like the disposal) is acceptable by the manufacturer.
Other than that, the only suggestion that I have is a switch or possibly a fusetron to the MC.
01-24-2008, 07:21 AM #3
01-24-2008, 07:40 AM #4
From the 2008 NEC (and not new to the 2008). (bold is mine)
- 314.29 Boxes, Conduit Bodies, and Handhole Enclosures to Be Accessible.
- - Boxes, conduit bodies, and handhole enclosures shall be installed so that the wiring contained in them can be rendered accessible without removing any part of the building or, in underground circuits, without excavating sidewalks, paving, earth, or other substance that is to be used to establish the finished grade.
- - - Exception: Listed boxes and handhole enclosures shall be permitted where covered by gravel, light aggregate, or noncohesive granulated soil if their location is effectively identified and accessible for excavation.
- Accessible (as applied to wiring methods). Capable of being removed or exposed without damaging the building structure or finish or not permanently closed in by the structure or finish of the building.
Thus, that installation *should not have been* installed as it was in the first place.
(I am assuming that your friend is the seller and not the buyer, the same advice applies if he - or she - is the buyer.)
01-25-2008, 02:30 PM #5
Many such water heaters either come with, or are intended for use with, a flexible cord and plug. In a sense, this is preferable, because the receptacle is then required to be GFCI protected. On the downside, 120 volt water heaters don't work so well.
Directly hard-wiring the unit may not require a disconnect; I believe the presence of locking tabs at the breaker fulfill the code LOTO requirements. In a similar manner, I believe that the use of NM (romex) is an approved wiring method. On the downside, a hard-wired unit is not required to have GFCI protection.
The real problem, as I see it, is the use of the plug with the NM. Having actually performed the tests, I can state quite simply that the plug's strain relief will not grip the NM well enough to pass the test ... so, sooner or later, the 'tug to unplug' is going to be transmittes to the wire connections - not a good thing.
01-25-2008, 03:01 PM #6
I was always under the impression that NM had to be protected. Going with that I have always terminated NM in a junction box, then used an appliance cord set or liquid tight conduit, or at least BX to go to appliance, along with the proper connectors at the J-box and the appliance. That's the way I was taught, vaguely remember NEC addressing such methods, but it's been a while since I really did much electrical, maybe I was wrong all this time........