04-15-2007, 03:49 PM #1
Discoloration on Insualtion of wires
04-15-2007, 04:07 PM #2
Re: Discoloration on Insualtion of wires
Jeff, any other visual evidence such as corrosion or melted insulation? Was the wire gauge properly sized for the serving breaker?
04-15-2007, 05:32 PM #3
Could not tell from the photo, but that is just the outer covering on THHN/THHW/etc., and it probably was not sunlight resistant and may have been left open for an extended time, or, possibly some type of clearner/solvent/lubricant was wiped on the conductor?
Only 90% sure from the photo, but I'd probably not say anything about that (unless there was something more to make me suspicious of another problem).
04-15-2007, 10:06 PM #4
I'd go with a powder or lubricant used at the installation.
I would not write that up alone.
