Results 1 to 11 of 11
Thread: panel location
01-28-2008, 05:58 AM #1
panel location
besides the obvious clearances what else is wrong with this as it pertains to exhaust flues etc?
Thanks!
01-28-2008, 06:13 AM #2
Re: panel location
B-vent "connected" to draft hood without proper adapter. Is this the same water heater with staining at the burner area?
01-28-2008, 06:22 AM #3
Re: panel location
Jerome,
You mean like:
- No Type B gas vent is allowed to be within 36" in front of the panel.
- No water pipe is allowed to be within 36" in front of the panel.
- No water heater is allowed to be within 36" in front of the panel.
But those are 'not allowed' because they encroach into the required 36" in-front-of-the-panel working space ... so it gets back to "the obvious clearances" you mentioned.
01-28-2008, 08:56 AM #4
Re: panel location
Jerry P
Wadda you mean clearance? It looks like it was the intention of the plumber to provide wireless bonding for the water heater's supply piping by putting it as close as possible to the electrical distribution panel? Don’t you agree that’s brilliant !
01-28-2008, 09:58 AM #5
Re: panel location
John,
According to the Simpson Dura-Vent website, an adapter is not required by the flue pipe manufacturer. However, it might be required by the water heater manufacturer.
Simpson Dura-vent (#12)
Simpson Dura-vent (#17)
01-28-2008, 01:58 PM #6
Re: panel location
Yes this is that same water heater
01-28-2008, 02:37 PM #7
Re: panel location
Too much wire sheathing inside the panel box.
And Isn't that romex wire coming out of the BX cable on the bottom of the box?
01-28-2008, 07:26 PM #8
Re: panel location
01-28-2008, 07:30 PM #9
Re: panel location
01-29-2008, 03:24 PM #10
Re: panel location
Besides the sloppy panel the NM cable is not protected on the walls.
But your question was (what else is wrong with the flue as to the picture) so I don't know if you are looking for help on other things wrong or trying to stump us on something that is wrong?
01-29-2008, 07:46 PM #11
Re: panel location
I think Jerome was asking about the vent in relation to the electrical panel, not necessarily the vent itself - such as if there was a requirement which did not allow the vent to be within some distance of a panel, and, to my knowledge, it could right next to it (but I would have a problem with that as it could overheat the panel and and insulation touching the panel enclosure).