Thread: 2 Q's on 3 flat
03-30-2008, 12:44 PM #1
2 Q's on 3 flat
One, should grounds be isolated from neutral bus on first panel (closest to service feed) and is there any problem with aluminum service neutral from Utility? Three 100 amp panels for each unit.
03-30-2008, 01:24 PM #2
Re: 2 Q's on 3 flat
Looks like service equipment. Neutral and grounds are required to be bonded together in the service equipment and separated at any downstream panels.
03-30-2008, 01:31 PM #3
Re: 2 Q's on 3 flat
Thanks GA.
03-30-2008, 01:38 PM #4
Re: 2 Q's on 3 flat
Both are fine.
Paul Kondzich
Ft. Myers, FL.
03-30-2008, 03:32 PM #5
Re: 2 Q's on 3 flat
Gunnar said "Looks like service equipment."
That is true ... *IF* ... that is the service equipment.
Let's clarify that it is ... the main disconnect in those panels are the first main disconnects, right?
No other disconnects ahead of them.
No 'main disconnect' for the service with these fed from that, right?
03-30-2008, 05:54 PM #6
Re: 2 Q's on 3 flat
JP,
He did say "service feed". I assume that if he meant "main disconnect" he would have said it. However, it wouldn't be the first time I've been wrong (today).
03-30-2008, 07:19 PM #7
Re: 2 Q's on 3 flat
To me ... that means there is the service ... and somewhere near there are those panels ... but (as I was asking) where are 'the first main service disconnects'?
In those panels or before those panels?