Results 1 to 6 of 6
  1. #1
    Richard Roshak's Avatar
    Richard Roshak Guest

    Default Exhaust fan is shower

    Are powered exhaust fans permitted in ceilings of showers. This one was not even GFI protected.

    Rich

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    OREP Insurance

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,042

    Default Re: Exhaust fan is shower

    Only if it is wet location rated, which is highly unlikely.

    Most shower fans I've seen are simply grilles with exhaust duct leading to a remotely mounted exhaust fan.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Ted Menelly's Avatar
    Ted Menelly Guest

    Default Re: Exhaust fan is shower

    Wet rated or not I have seen dips just in dryer vent lines running through the attic to a side wall that was not sealed and the water gathered at the dip and slowly destroyed the ceiling below. All that water from a shower (it has to be buckets) blowing thru a vent line I cannot see it not just running back down out of the vent to the shower unless it has a 427 hooked up to the fan.


  4. #4
    Jim Zborowski's Avatar
    Jim Zborowski Guest

    Default Re: Exhaust fan is shower

    Ted, I really don't think you'ld want a 427 hooked to the exhaust fan with the price of gas right now.........maybe a small block?


  5. #5
    Join Date
    Mar 2007
    Location
    georgia
    Posts
    112

    Default Re: Exhaust fan is shower

    that appears to be an older model broan fan/light the specs for those fans allow it if gfci protected. Fan/Light
    Model 657
    • 70 CFM 4.0 Sones.
    • Designer styled white polymeric grille complements virtually any decor.
    • Bright 100-watt light capacity.
    Bulb not included
    • 15-amp circuit acceptable.
    • Type IC (Insulation Contact).
    • Use with Model 68W or 68V two-function control (available separately).
    • UL Listed for use over bathtubs and showers when connected to GFCI-protected branch circuit.
    • Does not include heater.


  6. #6
    Mark Jones's Avatar
    Mark Jones Guest

    Default Re: Exhaust fan is shower

    I concur with Paul and Jerry. The exhaust fan units I've seen rated for use in a shower have an all plastic housing, or are required to be connected through a GFCI protected circuit.