Thread: GFCI outlets
07-25-2008, 08:22 AM #1
GFCI outlets
Can kitchen ranges be plugged into an outlet protected by a GFCI?
07-25-2008, 08:45 AM #2
Re: GFCI outlets
I assume it has a appliance cord on it to plug into a 110 receptacle, it must be to the electronic ignition for a gas range.
Yes, it could be connected to a GFCI.
07-25-2008, 02:22 PM #3
Re: GFCI outlets
Yep you got it. Thanks Rick.
07-25-2008, 05:13 PM #4
Re: GFCI outlets
210.52(B)(2) No Other Outlets. The two or more small-appliance
branch circuits specified in 210.52(B)(1) shall have no
other outlets.
Exception No. 1: A receptacle installed solely for the electrical
supply to and support of an electric clock in any of
the rooms specified in 210.52(B)(1).
Exception No. 2: Receptacles installed to provide powerranges, ovens, or counter-mounted cooking units.
for supplemental equipment and lighting on gas-fired
I tossed that in as I wasn't sure if the question was about GFCIs in general or the small-appliance (countertop) circuits. But...OK either way. One would hope that someone wouldn't turn on a cook-top burner and then run away before he noticed it didn't ignite.